I thought this was an interesting consideration from NICEIC Q and A on AFDDs. I would have thought the regulation was focused at what might end up connected to a socket rather than the AFDD protection for the circuit. Were that to be the case, then what about all the other circuits that do not have sockets?

Parents
  • The product standard for AFDDs states, in the scope:

    These devices are intended to mitigate the risk of fire in final circuits of a fixed installation due to the effect of arc fault currents that pose a risk of fire ignition under certain conditions if the arcing persists.

    (my highlight).

    Regulation 421.1.7 in BS 7671:2018+A2:2022 also relates to a provision for specific final circuits (and talks about the 'circuit to be protected') rather than, for example, Regulations 411.3.3, 708.415.1, 709.531.2, etc, which require RCDs to be provided for socket-outlets (not final circuits supplying socket-outlets).

    Were that to be the case, then what about all the other circuits that do not have sockets?

    Therefore, this is a really good question.

    The definition of a final circuit (and circuit) doesn't necessarily imply that circuits (or the effect of their protective devices) stops at accessories, connection units, or socket-outlets, and plugs and socket-outlets can be used for connection of fixed equipment (or portable or mobile) current-using equipment to circuits.

Reply
  • The product standard for AFDDs states, in the scope:

    These devices are intended to mitigate the risk of fire in final circuits of a fixed installation due to the effect of arc fault currents that pose a risk of fire ignition under certain conditions if the arcing persists.

    (my highlight).

    Regulation 421.1.7 in BS 7671:2018+A2:2022 also relates to a provision for specific final circuits (and talks about the 'circuit to be protected') rather than, for example, Regulations 411.3.3, 708.415.1, 709.531.2, etc, which require RCDs to be provided for socket-outlets (not final circuits supplying socket-outlets).

    Were that to be the case, then what about all the other circuits that do not have sockets?

    Therefore, this is a really good question.

    The definition of a final circuit (and circuit) doesn't necessarily imply that circuits (or the effect of their protective devices) stops at accessories, connection units, or socket-outlets, and plugs and socket-outlets can be used for connection of fixed equipment (or portable or mobile) current-using equipment to circuits.