When testing for earth contiuity is a tester that only delivers up to 200mA OK in every situation or should an instrument that has a 10A or 25A be used with certain loads or in certain types of bonding? Is this stated somewhere in the regulations?

I'm looking to ensure that some power supply units that are used are adequately earthed.  The units vary in load from <1kW to 15kW and have type 1 insulation class. The manufacturer recommends a bonding conuctor rated to carry 80A for the larger units. These PSUs are disconnected and moved from time ot time and I'd like to establish a guidance note for checking earth continuity when re-connected.

Parents
  • Way back at a time of the first iteration of the 2391 when the exam unceremoniously slaughtered the unsuitable and left the successful with a proud sense of merit, it was a commonly posed question to ask a candidate to describe the procedure for testing a suspected high resistance joint in a run of galvanised trunking.

    Marks were awarded for stating the correct instrument, which, according to City and Guilds, was a high current low resistance ohmmeter producing a maximum current of 25A at 40vAC. Results should not exceed 0.5ohms (all if memory serves me correctly).

Reply
  • Way back at a time of the first iteration of the 2391 when the exam unceremoniously slaughtered the unsuitable and left the successful with a proud sense of merit, it was a commonly posed question to ask a candidate to describe the procedure for testing a suspected high resistance joint in a run of galvanised trunking.

    Marks were awarded for stating the correct instrument, which, according to City and Guilds, was a high current low resistance ohmmeter producing a maximum current of 25A at 40vAC. Results should not exceed 0.5ohms (all if memory serves me correctly).