Cable Derating Factors - Single circuit, multiple cables in duct

I've been asked to size a cable for a large load - 630A.
With BS7671 in one hand and IET Electrical Installation Design Guide: Calculations for Electricians and Designers, 5th Edition in the other I'm working through the different derating factors.

The cable is not close to any other circuits so I'm working on the assumption that the Grouping Factor Cg is 1.0

Most of the other factors appear straightforward but there are two points that I'm not clear on...

"Buried Circuit Rating Factor" Cc 

Regulation 433.1.203 states
For direct buried cables or cables in buried ducts where the tabulated current-carrying capacity is based on an ambient temperature of 20 °C compliance with condition (iii) of Regulation 433.1.1 is afforded if the rated current or current setting of the protective device (In) does not exceed 0.9 times the current-carrying capacity (Iz) of the lowest rated conductor in the circuit protected.
Which suggests I need to derate the cable by 0.9

I've read the discussion (on this forum and elsewhere) and can see how this relates to the way that fuses operate, however, this circuit will be protected by a Schneider NSX630N MCCB which will trip when the load current >1.2 In after 100 seconds.

Consulting 433.1.1 (iii)
The current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit
Am I correct that I can set Cc to 1.0 for this installation?
Effect of running multiple conductors per phase
If Cc =0.9, then then for my 630A load, It > 700A
Based on four-core, copper, SWA cable, then we're looking at 3no 185mm2

As these are all feeding the same load am I correct that the Grouping Factor Cg is still 1.0?
Any issues with running the three cables in the same duct? (Apart from physically pulling them in of course!)
Many thanks
Parents
  • The derivation of Cc is given in the Commentary on IET Wiring Regulations if you have access to a copy (I would recommend a read to any designer working on your scale of project) but in short it's an adjustment for the temperature rise due to small overloads being different for buried cables due to a lower ambient temperature. The Cc value in the Regs is in fact a conservative value allowing for different cable types. Notably if you assume a lower ambient soil temperature, Cc gets "worse", but 0.9 covers the usual cases down to 15°C.

    You could if you wanted calculate Cc with project-specific values and still conform to BS7671 (since Cc as 0.9 is in the informative Appx 4, but the actual requirement is 433.1)... But unless your Client will be happy to show your design calculations to anyone reviewing the design for the life of the installation, it's probably not worth arguing, and at last check Amtech/Trimble (yes, other software exists) don't allow it do be varied so you'll be doing it by hand. Note that this way, Cc will likely not be 1.0, but may be greater than 0.90.

    Alternatively if you really do know your load well, it is fixed and it cannot suffer small overloads, such that overload protection can be omitted, so can Cc. (Mike's already written more about that)

    Meanwhile as already said, even if the cables are feeding the same load the grouping factor will be for three circuits.

    As for cables in the same duct (they're a bit big for it though!) there isn't a tabulated solution for multiple cables in a duct in Appx 4 so you need engineering judgement, some other set of tables, or to calculate from first principles (BS EN 60287). Or, more practically, use separate ducts for each cable (or trefoil/quad bundle).

Reply
  • The derivation of Cc is given in the Commentary on IET Wiring Regulations if you have access to a copy (I would recommend a read to any designer working on your scale of project) but in short it's an adjustment for the temperature rise due to small overloads being different for buried cables due to a lower ambient temperature. The Cc value in the Regs is in fact a conservative value allowing for different cable types. Notably if you assume a lower ambient soil temperature, Cc gets "worse", but 0.9 covers the usual cases down to 15°C.

    You could if you wanted calculate Cc with project-specific values and still conform to BS7671 (since Cc as 0.9 is in the informative Appx 4, but the actual requirement is 433.1)... But unless your Client will be happy to show your design calculations to anyone reviewing the design for the life of the installation, it's probably not worth arguing, and at last check Amtech/Trimble (yes, other software exists) don't allow it do be varied so you'll be doing it by hand. Note that this way, Cc will likely not be 1.0, but may be greater than 0.90.

    Alternatively if you really do know your load well, it is fixed and it cannot suffer small overloads, such that overload protection can be omitted, so can Cc. (Mike's already written more about that)

    Meanwhile as already said, even if the cables are feeding the same load the grouping factor will be for three circuits.

    As for cables in the same duct (they're a bit big for it though!) there isn't a tabulated solution for multiple cables in a duct in Appx 4 so you need engineering judgement, some other set of tables, or to calculate from first principles (BS EN 60287). Or, more practically, use separate ducts for each cable (or trefoil/quad bundle).