I was working on a job the other day where an e.on man was fitting a smart meter.
In converstion he told me that e.on were taking out any flexible tails they found fitted between the cut out, meter and any isolator installed.
From the meter or isolator, the customers 'tails' if flexible would of course be left installed.
Seeing as how I'm trying to save more wear and tear on my digits which are now suffering badly after years of bending 25 & 35mm2 'tails' I'll keep using flexible 'tails' untiil I'm told oficially a reason not to.
Apparently this doesn't apply to various other service providers.

Parents
  • I'll keep using flexible 'tails' untiil I'm told oficially a reason not to

    To be clear, whilst often advertised as such, e.g. https://www.cef.co.uk/catalogue/products/4626461-25mm-flexible-double-insulated-meter-tail-pack-1m, 19-strand tails are in fact Class 2 stranded circular conductors. BS EN 60228 only specifies the minimum number of strands for Class 2 conductors, being 7 for 25 sq mm and 35 sq mm csa. Whilst for Class 5 flexible conductors BS EN 60228 specifies only a maximum diameter of wires, this would lead to a minimum of around 190 strands for 25 sq mm csa and 266 strands for 35 sq mm csa.

    What's the issue, can they be used without special preparation?

    Well, that depends on what the terminal manufacturer has designed and tested for ... if it's the minimum in a standard, perhaps not.

Reply
  • I'll keep using flexible 'tails' untiil I'm told oficially a reason not to

    To be clear, whilst often advertised as such, e.g. https://www.cef.co.uk/catalogue/products/4626461-25mm-flexible-double-insulated-meter-tail-pack-1m, 19-strand tails are in fact Class 2 stranded circular conductors. BS EN 60228 only specifies the minimum number of strands for Class 2 conductors, being 7 for 25 sq mm and 35 sq mm csa. Whilst for Class 5 flexible conductors BS EN 60228 specifies only a maximum diameter of wires, this would lead to a minimum of around 190 strands for 25 sq mm csa and 266 strands for 35 sq mm csa.

    What's the issue, can they be used without special preparation?

    Well, that depends on what the terminal manufacturer has designed and tested for ... if it's the minimum in a standard, perhaps not.