Solar PV - Impact on rating of supply cables and transformer

We are in the process of getting some quotes for a solar PV installation on the roof of a large warehouse. The solar PV is probably going to be around 200kW

At the moment we are not connected to the grid and are waiting for new substation to be completed and cabling and transformers to be installed. 

One of the solar PV suppliers has said that we would need to add 200kW to our maximum demand figures when informing the DNO of our requirements which would probably take us to next size of transformer.

Can somebody point me in the right direction to read up about this or explain why the power from the solar PV generated  is added to the  max demand figures.

Thanks

Parents
  • One of the solar PV suppliers has said that we would need to add 200kW to our maximum demand figures when informing the DNO of our requirements which would probably take us to next size of transformer.

    While Mike is right that historically, and when roughtimating transformer sizes, people do sometimes look at it this way, the correct approach would be to specify the generation, and of this, the required export capacity, separately to demand, through the G99 application process. It should not be added like this on the maximum demand you have on your connection agreement.

    You may, for example, have an export (or, indeed, demand) limiting scheme in place, which might completely mitigate the voltage regulation issue, but would not necessarily save you considering other effects, like voltage step changes and harmonics. Conversely, depending on the equipment installed locally and design of the generator, there may be changes to other DNO equipment (e.g. reverse power or NVD protection)

    Your installer, or designer, should be able to assist with the G99 process. Often installers prefer to go through G99 after being contracted, unless you're paying them separately for it or they have preferred bidder status, but bear in mind that it may not be quick for a project of this scale and may even mean additional works beyond the transformer sizing. Noting that you seem to have started DNO works but haven't yet got a PV installer in contract, you presumably already have a contact with your DNO who might at least be able to give you a steer as to whether its liable to affect equipment sizing on-site now or whether you can pick an installer and apply for generation connection "at leisure".

Reply
  • One of the solar PV suppliers has said that we would need to add 200kW to our maximum demand figures when informing the DNO of our requirements which would probably take us to next size of transformer.

    While Mike is right that historically, and when roughtimating transformer sizes, people do sometimes look at it this way, the correct approach would be to specify the generation, and of this, the required export capacity, separately to demand, through the G99 application process. It should not be added like this on the maximum demand you have on your connection agreement.

    You may, for example, have an export (or, indeed, demand) limiting scheme in place, which might completely mitigate the voltage regulation issue, but would not necessarily save you considering other effects, like voltage step changes and harmonics. Conversely, depending on the equipment installed locally and design of the generator, there may be changes to other DNO equipment (e.g. reverse power or NVD protection)

    Your installer, or designer, should be able to assist with the G99 process. Often installers prefer to go through G99 after being contracted, unless you're paying them separately for it or they have preferred bidder status, but bear in mind that it may not be quick for a project of this scale and may even mean additional works beyond the transformer sizing. Noting that you seem to have started DNO works but haven't yet got a PV installer in contract, you presumably already have a contact with your DNO who might at least be able to give you a steer as to whether its liable to affect equipment sizing on-site now or whether you can pick an installer and apply for generation connection "at leisure".