Hi all,
I have a question if RCD's are required for 230v CCTV Cameras.
1. It is a TT system, resistance values unknown and not tested.
2. CCTV is fed from a 6A (MCB), SP&N DB, directly to a PSU which sits above the metallic camera column
3. Load is around 1A
4. Cable is 2.5mm singles within the metallic camera column, therefore daggling inside it.
Question is: do I require an RCD? Lightening protection has been risk assessed out, as it it not needed. If there is a break in the mains cable feeding the PSU, do I require an RCD? Resistance values from two points are less than 50ohms. Unfortunately an earth mat cannot be installed or electrode.
The client has also requested a CPC to the metallic column, but the main cables are protected. Is this the same principal as earthing a metallic back box within a domestic installation? I have looked at the BS761 regs for the answer, and I'm guessing as it's LV it may be required?
Please can someone advise?