Hi All,
Context
I'm mechanical by discipline and know enough to be dangerous about "the other side" but I need to put together a brief to get a main LV board replaced, never had to specify one before so feeling a bit out of my depth.
Main breaker is 1600A and is fed from a private sub on private wire HV network. The original Breaker is a Dorman Smith unit (area code doesn't have a 1 in it telling something about age)
The building is office however has some "technical" rooms with more complex requirements. (Parking the clean earth part for a moment).
There is also a "clean supply" which I assume is direct from the sub lv board (which has been contaminated with other supplies now) so we have two incomers.
Having read through the board types, a Form 4 would seem the appropriate category for a board such as this, beyond that I'm not sure what I should be asking for.
In the existing board there are about 10x100A isolators that are spare.
The building is subject to space being chopped and changed from office to technical spaces so, Ideally I'd want to be able to swap out isolators/circuit breakers with a correct size unit to match the load requirements as and when they present in the future.
Questions:
1). With having two supplies from a private network into the building this seems like bad practice to me due to the emergency isolation risk but I'm correct in thinking there is nothing in the current regs to prohibit this.
2). Having settled on a Form 4, what type should I got for given the need for future flexiblity, given I want to avoid having to take the LV board down to change/add supplies.
3). When would you typically use a Form 4 vs Form 3.
Thanks in advance for the help.