what JB/enclosure required for fire alarm installation

I am not an expert but re fire alarm systems but I need to split my fire loop due to modular project requires that.

Once the whole project delivered on site everything will be connected back and stays for years.

I have come across conflicting opinions about this.

Some say that this has to be done by using fire resistant plastic JB with ceramic terminals whereas other says that it need to be steel box not plastic.

I have fount both of them plastic and SS JB and they both actually "fire resistant" so I am confused completely.

  

Parents
  • Hi Tom,

    I think I can offer some help here, though just to be fully transparent I work for Hensel, one of the junction box manufacturers you’ve mentioned.

    To answer your question directly, if you need to use a junction box on a fire alarm system it’s important that the connection terminals inside it can withstand fire conditions for at least as long as the cable it's connecting.

    BS 5839-1 requires that fire alarm cables maintain integrity for a minimum of 30 minutes, and up to 120 minutes for enhanced systems. The standard also states that terminals must withstand similar temperature and duration as the cable.

    As you’ve noted, we have a fire-resistant range of polycarbonate enclosures that use ceramic terminals and an internal metal support plate, tested and approved to maintain circuit integrity for up to 2 hours (PH120). So although the outer enclosure is plastic, the whole system (including terminals and mounting) is designed and tested to perform under fire conditions.

    Since we already specialise in polycarbonate enclosures, we’ve been able to keep key benefits of our standard enclosures (like quick installation and cost-efficiency) and still meet the fire performance requirements set out in the standards.

    Hope that helps!

Reply
  • Hi Tom,

    I think I can offer some help here, though just to be fully transparent I work for Hensel, one of the junction box manufacturers you’ve mentioned.

    To answer your question directly, if you need to use a junction box on a fire alarm system it’s important that the connection terminals inside it can withstand fire conditions for at least as long as the cable it's connecting.

    BS 5839-1 requires that fire alarm cables maintain integrity for a minimum of 30 minutes, and up to 120 minutes for enhanced systems. The standard also states that terminals must withstand similar temperature and duration as the cable.

    As you’ve noted, we have a fire-resistant range of polycarbonate enclosures that use ceramic terminals and an internal metal support plate, tested and approved to maintain circuit integrity for up to 2 hours (PH120). So although the outer enclosure is plastic, the whole system (including terminals and mounting) is designed and tested to perform under fire conditions.

    Since we already specialise in polycarbonate enclosures, we’ve been able to keep key benefits of our standard enclosures (like quick installation and cost-efficiency) and still meet the fire performance requirements set out in the standards.

    Hope that helps!