what JB/enclosure required for fire alarm installation

I am not an expert but re fire alarm systems but I need to split my fire loop due to modular project requires that.

Once the whole project delivered on site everything will be connected back and stays for years.

I have come across conflicting opinions about this.

Some say that this has to be done by using fire resistant plastic JB with ceramic terminals whereas other says that it need to be steel box not plastic.

I have fount both of them plastic and SS JB and they both actually "fire resistant" so I am confused completely.

  

Parents
  • BS 5839-1:2025

    "35.4 Cables should be installed without external joints wherever practicable."

    BS 8519:2020

    17.1 "Where the life safety, fire-fighting or other critical circuits require the use ofjoints or junction boxes
    to house terminations and other critical system components, they should provide the same level of
    fire performance as that offered by the cable."

Reply
  • BS 5839-1:2025

    "35.4 Cables should be installed without external joints wherever practicable."

    BS 8519:2020

    17.1 "Where the life safety, fire-fighting or other critical circuits require the use ofjoints or junction boxes
    to house terminations and other critical system components, they should provide the same level of
    fire performance as that offered by the cable."