SIMULTANEOUS CONTACT QUESTION - 2 x EV vehicles parked next to each other

Scenario

A remote block of 3 garages, 2 will be fed from separate properties via 40m of 10mm EV SWA connected to 2 individual new CU's

( no cars will be parked inside the garages but charged on the drive in front of the garage door)

1 property is TNC-S - Ze 0.30 Ohms and the other is visually a TNS but with Ze 0.32 Ohms and similar L-N reading.

The 2 chargers will have Pen fault protection and the relevant RCD protection as usual.

There are underground services within 1 -10m of a potential TT rod so could be problematic and a maximum 2.5m between separate garage earth rods is possible.


The concern is simultaneous contact between the 2 vehicles.

Regulation 411.3.1.1 states that “simultaneously accessible conductive parts shall be connected to the same earthing system individually, in groups or collectively.”

I am currently waiting for UK Power networks to confirm the 2 properties are connected to the same earthing system.


The questions are:

Is Pen fault and RCD protection enough when connecting both cars to TNS/TNCS or is there anything else we can do?

Is separate TT earth rods along with simultaneous risk assessment the safest option in this case?

Thank you


I've attached a sketch of the current proposal to help explain.
PDF

Parents
  • Hi Dean. Have you managed to confirm with the DNO if both Properties Share the Same Earthing System ? 

  • just think the Properties having different Earthing Systems is unlikely. I know it’s possible. 

    It is critical to confirm whether both properties share the same earthing system. If they do, the vehicles will be at the same earth potential, eliminating concerns about simultaneous contact.

  • Hi Amk

    Thank you for your feedback.

    I haven't heard back from the DNO as yet, fingers crosses i get confirmation next week,

    If not condudisc TT option is the way to conform to 411.3.1.1.

    I will keep you posted.

Reply
  • Hi Amk

    Thank you for your feedback.

    I haven't heard back from the DNO as yet, fingers crosses i get confirmation next week,

    If not condudisc TT option is the way to conform to 411.3.1.1.

    I will keep you posted.

Children
No Data