SIMULTANEOUS CONTACT QUESTION - 2 x EV vehicles parked next to each other

Scenario

A remote block of 3 garages, 2 will be fed from separate properties via 40m of 10mm EV SWA connected to 2 individual new CU's

( no cars will be parked inside the garages but charged on the drive in front of the garage door)

1 property is TNC-S - Ze 0.30 Ohms and the other is visually a TNS but with Ze 0.32 Ohms and similar L-N reading.

The 2 chargers will have Pen fault protection and the relevant RCD protection as usual.

There are underground services within 1 -10m of a potential TT rod so could be problematic and a maximum 2.5m between separate garage earth rods is possible.


The concern is simultaneous contact between the 2 vehicles.

Regulation 411.3.1.1 states that “simultaneously accessible conductive parts shall be connected to the same earthing system individually, in groups or collectively.”

I am currently waiting for UK Power networks to confirm the 2 properties are connected to the same earthing system.


The questions are:

Is Pen fault and RCD protection enough when connecting both cars to TNS/TNCS or is there anything else we can do?

Is separate TT earth rods along with simultaneous risk assessment the safest option in this case?

Thank you


I've attached a sketch of the current proposal to help explain.
PDF

Parents
  • Dean,

    Obviously as you have indicated and good advice from Graham, and maybe its a remote option that could be considered.

    And that would be to install or erect some kind of "Wall/partition" between the two EV charging bays, to prevent similtaneous contact? Might not look pretty and obviously something a car could hit if not being carefull, but if done correctly could perhaps give an option if UKPN confirm the worst, just need to consider the fire rating and combustible nature of any "Wall/partition".

    Cheers GTB 

  • Hi Graham

    Thank you for this info.

    I contacted earthing services today ( very helpful guy), he said with one separate condudisc/earthing conductor per garage situated 2.5m apart and connected together in the ground at 600mm will achieve 53 Ohms( with this post codes soil resistivity).

    He also said if one client disposes of their charger/garage supply it still leaves the other with a 53 Ohms earth resistance.

    The condudisc has a life expectancy of 408 years if embedded in conductive concrete, would this be an compliant option if UKPN do not commit?

    Kind regards

    DeanW

  • I have just checked my home insurance policy booklet.  No mention of RC59.  No mention of car chargers at all.  No mention of what sort of fences I am allowed to have.  Not that they cover damage to fences for any reason.

    I often see on various forums that people say "if you do X, your insurance will be invalid", or "if you don't do Y then your insurance will be invalid".  And the vast majority of times, the policy doesn't even mention X or Y.

  • Morning Simon,

    Im not the type of person to indicate something on a forum that is just made up or indeed will be unhelpful to the enquirer. As Graham mentioned its not a BS7671 issue albeit the electrical designer does need to take into account the environment and use to which the einstallation and equipmet will be used. RC59 isnt mandatory norcarry any legal authority. It is however produced and devloped by the UK's major insurance companies.

    There may be no wording on your own policy, but there are on others and changes in terms and conditions are starting to trickle through in policy updates when renewal time comes round.

    I have enclosed below detail from Zurich Insurance, so the terms and conditions simply stated in small print that if the "Property" has EV charging facilities then the detail in the guide should be considered.

    Now, I would have thought any project should have somebody considering any fire risk changes, then eliminating or if not mitigating them and believe thats whats in this document.

    I suspect like all insurance policies, its not until you claim, then you find out there is an issue in cover provided or worse total rejection of the claim, as we all know its the policy holders responsibility to ask or notify changes to the insurer and they will then advise on what they believe should be done.

     A good electrical designer, electrical engineer or contractor I would have hoped will have at least touched on the subject with their client. 

    I never once said I dont believe insurance would be invalid, and if the policy doesnt mention something usually insurance stance is it wasnt covered.

    Cheers GTB

    PDF

  • He also said if one client disposes of their charger/garage supply it still leaves the other with a 53 Ohms earth resistance.

    The point I was making wasn't simply about "disposal" of one earthing system, but more the maintenance of the bond between the two if the two chargers are to keep operating under the same conditions.

  • It does not even need to be a long partition - 1.25 m should be enough.

    I assume, of course, that there is no rule which forbids the EVs to be simultaneously accessible.

  • I assume, of course, that there is no rule which forbids the EVs to be simultaneously accessible.

    Not sure what is meant by 'rule', but if the EVs are not connected to the same earthing system, ADS according to BS 7671 is not guaranteed to be safe. See Regulation 411.3.1.1 ?

  • I used the word, "rule" loosely to include statutory requirements, HSE advice, British Standards, etc.

    As far as I can see, whilst BS 7671 applies to EVCPs (101.1.1(xxiii)), the vehicles themselves are out of scope, but I may be wrong.

  • ADS according to BS 7671 is not guaranteed to be safe

    Graham,

    Could you set out an example?

  • I used the word, "rule" loosely to include statutory requirements, HSE advice, British Standards, etc.

    OK, well if the 'etc' covers the IET Code of Practice for EV Charging Equipment Installation, which is cited by OZEV and Part S guidance, then yes, there is a 'rule' that covers this.

    As far as I can see, whilst BS 7671 applies to EVCPs (101.1.1(xxiii)), the vehicles themselves are out of scope, but I may be wrong.

    Yes ... but no ... Unfortunately, whilst BS 7671 covers the EV charging points, the fact remains that, when the vehicle is connected, the potentials at the exposed-conductive-parts of the EV charging point are transferred to the exposed-conductive-parts of the EV through the cpc in the vehicle connecting lead.

    If we accept as fact that simultaneously-accessible exposed-conductive-parts of EV charging points pose a risk if they are not connected to the same earthing system, the fact must also be true of any protective conductors and exposed-conductive-parts connected to the EV charging points that are also simultaneously-accessible.

    This logic is also validated through Regulation 722.411.4.1, which is fully intended to prevent transfer of potentials that appear on protective conductors in the installation due to PEN conductor faults in the supply from being transferred to the exposed-conductive-parts of the vehicle.

  • As far as I can see, whilst BS 7671 applies to EVCPs (101.1.1(xxiii)), the vehicles themselves are out of scope, but I may be wrong.

    Yes ... but no ... Unfortunately, whilst BS 7671 covers the EV charging points, the fact remains that, when the vehicle is connected, the potentials at the exposed-conductive-parts of the EV charging point are transferred to the exposed-conductive-parts of the EV through the cpc in the vehicle connecting lead.

    This is where the situation with EVs can get absurd. Naturally, the electrons take the path of least resistance (pun intended) and could not care less about man-made rules.

    So we think that these two properties share the same TN-C-S (?) earthing system, but what about two TT cottages in the countryside?

Reply
  • As far as I can see, whilst BS 7671 applies to EVCPs (101.1.1(xxiii)), the vehicles themselves are out of scope, but I may be wrong.

    Yes ... but no ... Unfortunately, whilst BS 7671 covers the EV charging points, the fact remains that, when the vehicle is connected, the potentials at the exposed-conductive-parts of the EV charging point are transferred to the exposed-conductive-parts of the EV through the cpc in the vehicle connecting lead.

    This is where the situation with EVs can get absurd. Naturally, the electrons take the path of least resistance (pun intended) and could not care less about man-made rules.

    So we think that these two properties share the same TN-C-S (?) earthing system, but what about two TT cottages in the countryside?