SIMULTANEOUS CONTACT QUESTION - 2 x EV vehicles parked next to each other
Scenario
A remote block of 3 garages, 2 will be fed from separate properties via 40m of 10mm EV SWA connected to 2 individual new CU's
( no cars will be parked inside the garages but charged on the drive in front of the garage door)
1 property is TNC-S - Ze 0.30 Ohms and the other is visually a TNS but with Ze 0.32 Ohms and similar L-N reading.
The 2 chargers will have Pen fault protection and the relevant RCD protection as usual.
There are underground services within 1 -10m of a potential TT rod so could be problematic and a maximum 2.5m between separate garage earth rods is possible.
The concern is simultaneous contact between the 2 vehicles.
Regulation 411.3.1.1 states that “simultaneously accessible conductive parts shall be connected to the same earthing system individually, in groups or collectively.”
I am currently waiting for UK Power networks to confirm the 2 properties are connected to the same earthing system.
The questions are:
Is Pen fault and RCD protection enough when connecting both cars to TNS/TNCS or is there anything else we can do?
Is separate TT earth rods along with simultaneous risk assessment the safest option in this case?
Thank you
I've attached a sketch of the current proposal to help explain.
PDF
  • This is interesting, because the particular job this original thread refers, the garages are a wooden structure! Seems like everything is against this job.
    What happens in that case?
  • What happens in that case?
    Some insurers have terms that require a certain distance from combustible materials [some include shrubs, trees etc in that definition] from which EVs must be when on charge.
    The IET Code of Practice refers to an industry publication RC59 Fire safety when charging electric vehicles, which can be freely downloaded here: https://www.thefpa.co.uk/advice-and-guidance/free-documents?=%20Medium-sized%20Businesses,%20MAINTENANCE%20CHECKLISTS%20-%20APPENDIX%20TEMPLATE%20FORMS,%20CONTROL%20OF%20DUST%20EXPLOSIONS&q=RC59%20FIRE%20SAFETY%20WHEN%20CHARGING%20ELECTRIC%20VEHICLES
    The difficulty for designers is that insurance company terms vary, and they don't all align fully to RC59 ... so this is something that should be discussed with the Client(s) prior to the design being finalised.
  • Hi Graham
    Thank you for this info.
    I contacted earthing services today ( very helpful guy), he said with one separate condudisc/earthing conductor per garage situated 2.5m apart and connected together in the ground at 600mm will achieve 53 Ohms( with this post codes soil resistivity).
    He also said if one client disposes of their charger/garage supply it still leaves the other with a 53 Ohms earth resistance.
    The condudisc has a life expectancy of 408 years if embedded in conductive concrete, would this be an compliant option if UKPN do not commit?
    Kind regards
    DeanW
  • Hi Mike
    Agreed, as installers we need discussions like this, more and more people are taking up EV's and the overlaps are inevitable.
    DeanW
  • I have just checked my home insurance policy booklet.  No mention of RC59.  No mention of car chargers at all.  No mention of what sort of fences I am allowed to have.  Not that they cover damage to fences for any reason.
    I often see on various forums that people say "if you do X, your insurance will be invalid", or "if you don't do Y then your insurance will be invalid".  And the vast majority of times, the policy doesn't even mention X or Y.
  • I am rather surprised that this issue has not be raised before. Is it not inevitable?
  • Morning Simon,
    Im not the type of person to indicate something on a forum that is just made up or indeed will be unhelpful to the enquirer. As Graham mentioned its not a BS7671 issue albeit the electrical designer does need to take into account the environment and use to which the einstallation and equipmet will be used. RC59 isnt mandatory norcarry any legal authority. It is however produced and devloped by the UK's major insurance companies.
    There may be no wording on your own policy, but there are on others and changes in terms and conditions are starting to trickle through in policy updates when renewal time comes round.
    I have enclosed below detail from Zurich Insurance, so the terms and conditions simply stated in small print that if the "Property" has EV charging facilities then the detail in the guide should be considered.
    Now, I would have thought any project should have somebody considering any fire risk changes, then eliminating or if not mitigating them and believe thats whats in this document.
    I suspect like all insurance policies, its not until you claim, then you find out there is an issue in cover provided or worse total rejection of the claim, as we all know its the policy holders responsibility to ask or notify changes to the insurer and they will then advise on what they believe should be done.
     A good electrical designer, electrical engineer or contractor I would have hoped will have at least touched on the subject with their client.
    I never once said I dont believe insurance would be invalid, and if the policy doesnt mention something usually insurance stance is it wasnt covered.
    Cheers GTB
    PDF
  • He also said if one client disposes of their charger/garage supply it still leaves the other with a 53 Ohms earth resistance.
    The point I was making wasn't simply about "disposal" of one earthing system, but more the maintenance of the bond between the two if the two chargers are to keep operating under the same conditions.
  • Just looking at this discussion from a practical point of view with  a view to ADS.
    The supply to the EV charge points will have RCD protection on their supply, probably also a built in RCD. They will also have open pen detection, which should mean that if there was a significant issue with earthing due to an open pen conductor they should shut down. The RCD protection means that there only needs to be 30mA flowing to earth for the RCD to trip, I am struggle to think of a scenario where there would be a situation where the earthing of the two properties is separated to such an extent that 30mA will not flow under fault conditions, especially with open pen detection in place.
    I can see that where RCD protection is not included and much higher currents are required for ADS having a guaranteed common earth is sensibly required.
    Another approach that could be considered is looking at Indra chargers, they have an operating mode where they measure the voltage difference between their main earth and a reference electrode, if this increases beyond 30V the charger shuts down.
  • It does not even need to be a long partition - 1.25 m should be enough.
    I assume, of course, that there is no rule which forbids the EVs to be simultaneously accessible.