SIMULTANEOUS CONTACT QUESTION - 2 x EV vehicles parked next to each other

Scenario

A remote block of 3 garages, 2 will be fed from separate properties via 40m of 10mm EV SWA connected to 2 individual new CU's

( no cars will be parked inside the garages but charged on the drive in front of the garage door)

1 property is TNC-S - Ze 0.30 Ohms and the other is visually a TNS but with Ze 0.32 Ohms and similar L-N reading.

The 2 chargers will have Pen fault protection and the relevant RCD protection as usual.

There are underground services within 1 -10m of a potential TT rod so could be problematic and a maximum 2.5m between separate garage earth rods is possible.


The concern is simultaneous contact between the 2 vehicles.

Regulation 411.3.1.1 states that “simultaneously accessible conductive parts shall be connected to the same earthing system individually, in groups or collectively.”

I am currently waiting for UK Power networks to confirm the 2 properties are connected to the same earthing system.


The questions are:

Is Pen fault and RCD protection enough when connecting both cars to TNS/TNCS or is there anything else we can do?

Is separate TT earth rods along with simultaneous risk assessment the safest option in this case?

Thank you


I've attached a sketch of the current proposal to help explain.
PDF

Parents
  • Just looking at this discussion from a practical point of view with  a view to ADS.

    The supply to the EV charge points will have RCD protection on their supply, probably also a built in RCD. They will also have open pen detection, which should mean that if there was a significant issue with earthing due to an open pen conductor they should shut down. The RCD protection means that there only needs to be 30mA flowing to earth for the RCD to trip, I am struggle to think of a scenario where there would be a situation where the earthing of the two properties is separated to such an extent that 30mA will not flow under fault conditions, especially with open pen detection in place.

    I can see that where RCD protection is not included and much higher currents are required for ADS having a guaranteed common earth is sensibly required.

    Another approach that could be considered is looking at Indra chargers, they have an operating mode where they measure the voltage difference between their main earth and a reference electrode, if this increases beyond 30V the charger shuts down.

Reply
  • Just looking at this discussion from a practical point of view with  a view to ADS.

    The supply to the EV charge points will have RCD protection on their supply, probably also a built in RCD. They will also have open pen detection, which should mean that if there was a significant issue with earthing due to an open pen conductor they should shut down. The RCD protection means that there only needs to be 30mA flowing to earth for the RCD to trip, I am struggle to think of a scenario where there would be a situation where the earthing of the two properties is separated to such an extent that 30mA will not flow under fault conditions, especially with open pen detection in place.

    I can see that where RCD protection is not included and much higher currents are required for ADS having a guaranteed common earth is sensibly required.

    Another approach that could be considered is looking at Indra chargers, they have an operating mode where they measure the voltage difference between their main earth and a reference electrode, if this increases beyond 30V the charger shuts down.