SIMULTANEOUS CONTACT QUESTION - 2 x EV vehicles parked next to each other
Scenario
A remote block of 3 garages, 2 will be fed from separate properties via 40m of 10mm EV SWA connected to 2 individual new CU's
( no cars will be parked inside the garages but charged on the drive in front of the garage door)
1 property is TNC-S - Ze 0.30 Ohms and the other is visually a TNS but with Ze 0.32 Ohms and similar L-N reading.
The 2 chargers will have Pen fault protection and the relevant RCD protection as usual.
There are underground services within 1 -10m of a potential TT rod so could be problematic and a maximum 2.5m between separate garage earth rods is possible.
The concern is simultaneous contact between the 2 vehicles.
Regulation 411.3.1.1 states that “simultaneously accessible conductive parts shall be connected to the same earthing system individually, in groups or collectively.”
I am currently waiting for UK Power networks to confirm the 2 properties are connected to the same earthing system.
The questions are:
Is Pen fault and RCD protection enough when connecting both cars to TNS/TNCS or is there anything else we can do?
Is separate TT earth rods along with simultaneous risk assessment the safest option in this case?
Thank you
I've attached a sketch of the current proposal to help explain.
PDF
  • The RCD protection means that there only needs to be 30mA flowing to earth for the RCD to trip, I am struggle to think of a scenario where there would be a situation where the earthing of the two properties is separated to such an extent that 30mA will not flow under fault conditions, especially with open pen detection in place.
    There are several possibilities - the 30mA RCD protection typically only covers the final circuit (or possibly the charge point itself) - so earth faults upstream of the RCD (e.g. on submains or even in  DNO cables) will also cause a rise of potential on the earthing system, and may well take up to 5s to clear (for current BS 7671 installations, potentially longer for older ones, perhaps into minutes for some DNO faults). Even faults in neighbouring installations can drag a shared earthing system (e.g. via DNO facility or bonding of shared metallic pipework) to hazardous voltages for hazardous lengths of time.  Same reason we still need main bonding even when every final circuit has 30mA RCD additional protection.
  • I'm not a legal professional, but this arrangement of "shared earth" probably needs legal advice (what if one owner removes their charger, and the means of earthing ... leaving the other without a means of earthing, for example)?
    I suppose it's not that different, legally, from a lot of existing situations were one property relies on drains buried under (and shared with) neighbouring ones, or cables crossing a third party's land. Wayleaves for such things are very common, presumably it just needs someone to come up with an appropriate set of words.
    At least no-one has suggested installing individual isolating transformers and making each charge point "separated" (or rather not quite separated as there has to be a N-c.p.c. link to fool the EV & EVSE earthing checks).
    One day the vehicle manufacturers will get involved in these discussions and we'll end up with Class II EVs (like most other outdoor electrical equipment),
  • ADS according to BS 7671 is not guaranteed to be safe
    Could you set out an example?
    I suspect Graham had in mind some of the well known gaps ... for instance: the 0.4s (or 0.2s) disconnection time figures are all based on an assumption of body resistance values that only hold true for around 95% of the population ... for the other 5% there's an amount of luck involved if they're to survive such an event. The 0.4 (or 0.2s) ADS figures themselves only apply to smaller final circuits - higher rated circuits and distribution circuits are permitted longer disconnection times (and often do, to provide discrimination) - and earth faults on these circuits can raise the potential of the earthing system (including exposed-conductive-parts on final circuits) to hazardous voltages with no "safe" (ish) time limit. Main bonding is meant to mitigate the risks, but as there's no actual requirement for what it has to achieve - the overall effects will vary and may well not be enough to guarantee anything. Plus of course the risk of the first (undetected) fault being a broken c.p.c., or a stuck RCD. (Allegedly around 7% of installed RCDs won't perform as intended.)
    It all depends on what you mean by "safe" of course... guarantee that no harm will ever occur, or just the costs (in life, limb and damage to property) aren't too excessive.
  • Yep, a couple of years ago I had +180v between an outside tap and earth in one rural property connected to a TNCS earth. Turned out to be a fault to structural steel in a barn on a nearby farm that was connected to the same tx but as a TT system. The farm had only one RCD at the intake which failed to trip. The 180v was the voltage drop across the DNO electrode. That particular fault was evident for months, with the TNCS householder getting shock sensations. The DNO investigated but washed their hands of it when they confirmed it wasn’t open pen.
    I am not sure if I have a handle on all possible risks with simultaneous contact between EVs on separate earthing systems, but it seems illogical to expect neighbour A to have an EV charge point while neighbour B can’t because of what might be a relatively low risk.
  • Actually I thought we had discussed this before, and indeed we have
    And we dd not really resolve it very well then either,.
    Personally I still think as I thought then, that chargers will magically appear, the earthing question will not always be considered rigorously, so many installations may not meet the regs, and it will all work just fine most of the time, so it wont be strongly enforced.
  • Personally I still think as I thought then, that chargers will magically appear,
    As with charging caravans on driveways, some people won't care (or won't know).
    That's not necessarily the case ... 'cross-pavement charging' is bringing this to the forefront of people's minds now.
    Until the "it will never happen" happens (because we will have very large numbers of EVs on charge soon) and then the poor electricians who did the job could well be hauled over the coals for it, because they didn't conform to the standard.
  • Until the "it will never happen" happens
    That is always  risk - see the 'never happens' broken neutral debate -  and I'd like to hope that most installers will think and act sensibly. I'm also well aware , that here in the European western world we enjoy a very high, but also relatively very expensive, standard of electrical professionalism, and there is a long way for things to descend before plugging something in actually becomes comparably dangerous to most other human activities. There are however many places where this is true...
    It may be that to accelerate the roll-out of energy efficiency and 'Green' technology generally,  without needing to dig up every lawn or footpath first, there is a need to lighten up in some areas, on what we consider acceptable standards to be . Consider if class 1 heat pumps appear outside houses near neighbours. (do they warrent OPEN-like cover too ?). Do we encourage more casual or even DIY installation ? We might need to if the water levels get too deep...
    Actually the very existence of an OPEN device compared to a few years ago, is an example of that kind of re-think for the rules at the consumer end, and the widening of the grid rate of frequency slew tolerances is an example of similar (& sensible in my view) pragmatism at the generation end.
    I realise this is a sidetrack from the original topic, but it is possible that during the life of the installation, the rules regarding who can do what with earthing could change quite a bit, based on what has already happened during the last 50 years or so.
    (A variation on rules are shaped by the requirements of society - not just society being shaped by its rules.)
  • Hi
    Really intersting point regards the issue of possible voltage offsets. How do you view some of the present issues with cars being charged near street furniture but being supplied by a domestic property. The potential here is the fact the house is on a PME and the lampost a dedicated TN-S. The car is within the 2.5 metre distance so simultaneous contact is possible.
    Just for my own clarity as well - I see a lot of comments around the 2 earthing systems and the possible issues with ADS, what are the other concerns here if you do not mind me asking? In respects to how you view the faults, what are the risks in simple terms? The more I look at this issue the more I find it impossible to offer a solution.
  • Consider if class 1 heat pumps appear outside houses near neighbours. (do they warrent OPEN-like cover too ?)
    And the rules on where you can site a heat pump have now been relaxed, so it's possible to have two houses' heat pumps within touching distance of each other.
  • Will we see O-pen protection on heat pumps soon??? And the same issues we are having with SC that we have with EV?