Thoughts on Temporarily Paralleling Two 1600A ACBs with a Bypass Castell Key?
Hi everyone,
Looking for some insights on a proposed electrical setup and potential risks. We have a single LV switchboard with two 1600 Amp ACBs, each fed by separate transformers but connected to the same HV ring main. Both ACBs are equipped with Castell keys for interlocking. Normally, if one transformer fails, the procedure is to switch off its ACB, remove the Castell key, and close a bus coupler to maintain supply.
We need to perform some HV maintenance, which requires isolating each transformer one at a time. To avoid any supply interruption, there’s a suggestion to use a bypass Castell key to temporarily parallel the two supplies for a few seconds. The idea is to parallel the transformers, then switch off one ACB, keeping the load live throughout.
Has anyone done something similar or seen issues with this approach? Keen to hear your thoughts and experiences!
 Thanks -Andy
  • Paralleling identical transformers is done all the time, as is the related problem synchronizing generation to feed back into the supply. However, normally only when designed with this in mind from the outset, and the makers have supplied the instructions,
    Any difference in the two voltages will lead to serious circulating current -potentially both on the LV and HV side. Accurate measurements of the difference in secondary voltage and knowledge of the geometry of interconnecting cables and busbars, and so their resistance, will allow you to estimate how much one transformer will push back into the other.
    During the parallel period, what is the PSSC, and if a fault occurred, would anything be subjected to stresses out of spec?
    NE bonds, where are they and could switching like this introduce a floating condition where a transformer secondary loses its earth reference, while the primary remains alive? This is not good as the secondary tends to drift up to a good fraction of the HV voltage..
    I'd be more than a bit nervous without some top cover from someone who knows the design intimately.
  • The chief danger you have, is that the fault level will double, and it's unlikely the main switchgear (and design as a whole) has taken the double fault level into account ... if a fault were to occur during the time the transformers were in parallel, it could be a huge disaster, for example if the primary switchboard couldn't contain the fault level. If anyone were nearby the fault, and/or any equipment that was destroyed by the increased fault level, they might be seriously (or fatally) hurt.
    Therefore, unless all of the possible outcomes are worked through, as  says, by someone with full details of the design and equipment, I would be extremely wary of this approach.
    The usual approach to avoiding temporary supply interruption to key equipment, is to provide UPS ... if that has not been done, it seems like the design approach might have been for temporary shutdown in maintenance ... perhaps that is what is needed?
    As this maintenance is 'construction work' as defined, it's paramount the Client, and/or tenant, are fully aware of their duties in ensuring the maintenance is carried out safely - it's not simply down to the 'maintainer' to make this safe, and a requirement of 'power must stay on' might not be achievable if this hasn't been originally designed for.
  • As already siad above the proposal is risky.
    You would aboslutly have to veify the 2 supplies have the same phase rotation and phase sequence. As alreay said there could be an issue with supply impedences and voltages leading to circulating currents.
    As GK said 2 supplies may very well exceed the short circuit rating of the panel, bus bars and circuit protection.
    I saw an installation where there were 2 transformers supplies suppyling a very large Form 4 panel with a bus coupler in the middle with no Castell interlocking of the 2 supplies and the bus coupler. I asked the AP if they had put the bus coupler in and he said no, I said if you are thinking about doing it let me get far away before you do, I did specify the refuge location but that would be giving the location away.
    The interlocks are there for safety so overcoming a safty device is dangerous and possibly criminal. Find some other way would be my advice.
    JP
  • Thank you for the responses. I agree with points about circulating currents etc.
    The senior AP, from external contractors overseeing the HV maintenance, has stated that it’s common practice elsewhere to bypass the standard procedure (switching off one ACB, removing the Castell key, and closing the bus coupler). Instead, they routinely leave both ACBs energised, use a bypass Castell key to temporarily parallel the transformers for a few seconds, and then immediately switch off one ACB to avoid supply interruption. They claim this is standard in their operations and has been done without issues. I have checked phase rotation, and there’s no potential difference between phases of each busbar(Tx 1 - Tx 2)
    Despite this, I’m still against proceeding with this approach.  Am I  being overly cautious ?, but given the potential consequences, I’d rather err on the side of safety. We’re responsible for issuing a permit to work per HTM 06-02 for the work. I’m not convinced this procedure meets that standard. Thanks again for the input!
  • You mention that you are referencing HTM 06-02 so I assume it is a hospital?
    You are going to need a site specific Risk Assessment and Method Statement for this activity.  Comptencies of individuals and PPE will need addressing.
    JP
  • Hi AMK,
    Your external contractors may be indicating to yourself that its "Common Practice" but others may call that action a "Bad Habit"!!!!  Just because they say its common practice doesnt mean to say its actually correct and compliant. Reads as being far too risky to me, a few seconds doesnt matter, thats enough for something to go catastrophically wrong given the right set of the wrong circumstances.
    Cheers GTB
  • You would absolutely have to verify the 2 supplies have the same phase rotation and phase sequence.
    Indeed - cock that up and you are probably looking at waiting until something on the HV side lets go, and kills power to the site, and possibly a court appearance and a funeral to attend as well.
    This reminds me that I have memories of standing next to the twisted metal of some large switch-gear that had been taken back to the old "Brush" plant  near Leicester for investigation, while a number of studious chaps peered at it hopefully rather in the manner of air-crash investigators.
    The finer details of what had happened to get it like that had better remain under wraps, but basically due to a mix up about supplies. the fault current was at a level where the breaker could not actually break, and some other things were a bit slow on the uptake, and the arc had kept that current flowing for some seconds. The design lacked the (in my mind obligatory) 'death or glory' fuses at the incomer.  They are needed only for just this sort of thing.
    It really did look very much as if a small bomb had gone off, nearly all the strain flaps had actuated - there are deliberate weak points in the enclosure that yield to allow the expanding hot gas and vapourised metal to escape without, hopefully, pushing the front panel in the direction of the operator, and instead directing the worst of the fireball out of the top and to a degree the sides.
    Imagine the fairly heavy steel bulging alarmingly with inside-out crumple zones -don't under-estimate the power of the mis-placed electrons.
    In terms of the OP, unless it can be proven that the design is quite safe to be operated like that, whatever the contractors may do at other places, the sensible advice has to be 'don't '.
  • Subject to a detailed check that both supplies have the same phase rotation, phase sequence, and are reasonably close in voltage. then it would probably be fine. But is "probably" good enough ? perhaps not if one remembers just how destructive and even fatal the consequences could be.
    I have done as described, more than once, without ill effect, and I am still alive. But the fact that I have got away with it, does not prove that so doing is sensible.
    The main risk is the near doubling of fault current, when the two transformers are briefly paralleled. It is very unlikely that a fault would occur during this brief interval. But is the risk "low enough" ?
  • I endorse everything that has been said. The interlock is there for a reason.  Having said that I cant think of a reason why you couldnt check whether the equipment could be safely used in this way.  This isnt a comprehensive list but you would need to calculate the worst case fault levels and check installation details such as cable sizes and lengths.  I would also want to talk to the switchboard manufacturers re fault levels etc and check that appropriate terminations etc had been made. There is also the matter of the fault capability of downstream equipment. If there are two transformers fed from a single HV source or ring (with open point) the fault level wont be as high as if there are two independent supplies.
    This might all be worthwhile if the disruption caused by a switch off is severe but if that were the case you have to ask why it wasnt designed in in the first place.
  • There is always the extra risk, not well covered in the safety literature, that for any temporary works and unusual arrangements, that there are many layers of protection from the Swiss cheese model that have been implicitly removed by the "it'll be alright" assumptions we all make (esp those that say they don't ;-). Most Swiss cheese approaches cover normal running and common failures (until the unusual happens).
    It'll be a "Normal Accident" (Perrow) once it's happened. Reason's "Human Error" is also a good read for how these slips, lapses, and mistakes occur.
    Also beware of the 'false' "What's the worst that could happen" being discussed here which are local technical issues (nasty big bangs), rather than also considering the consequential 'worst that could happen' - e.g. Heathrow shut down et.al. vs small(ish) transformer fire. If it's a Hospital supply the minor slip-up becomes big news