Morning all, I'm just clearing up a discussion I've had at work. I'm still working through my qualifications so I'm going to assume I'm the wrong wrong here.
when testing several 3 phase boards and their respective fault currents if we had 3 boards supplied from the origin, I'd still test the pfc at each board and not just the origin of supply or is it just the origin and that's our pfc for the paper work for each board?