In the UK is your Domestic dwelling correctly protected by the SPD fitted in the CU/DB

BS7671 regulation 534.4.5, mandates that SPDs be protected against overcurrent via an MCB or Fuse
I think there are some other regulations which also state MCB/fuse protection is a requirement like


BS7671 reg 534.4.4.1.5
BS7671 reg 533.2.1
4BS7671 reg 34.5.1
BS7671 reg 712.534.101

This in my opinion goes against claims like the following and probably needs to be made clearer to the manufacturers, I would also suggest that BS7671 and GN (Guidance Notes) make this more clear for the Designer and Installer.
proteusswitchgear.com/.../

There are other manufactures also stating "No requirement for MCB" Proteus just happened to be the first my internet search engine came up with.


As always please be polite and respectful in this purely academic debate.

Come on everybody let’s help inspire the future.

Parents
  • I am not sure that SPDs contain their own built-in fuse in UK models

    As I understand it, the ones that don't require individual overcurrent protection do contain some kind of internal over current protection - but to many eyes it might not look like a conventional "fuse" - more like a bit of springy metal held closed with a blob of solder. As long as it melts before the SPD overheats to the point of being a hazard, my gut feel is that its probably OK.

    Personally I've always been a bit unsure of putting a device that's meant to reliably divert kA in series with a B32 or B16 MCB -  what are the chances of the MCB tripping and leaving the installation unprotected from subsequent surges, unbeknown to the householder?

      - Andy.

  • what are the chances of the MCB tripping and leaving the installation unprotected from subsequent surges, unbeknown to the householder?

    That's why the SPD is supposed to have a window, or other means of indicating "end of life".

  • On the simple wylex/crabtree types, that indicator window is usually held up against a spring, by the bit of fusewire (*)that evaporates when the SPD goes short circuit, then the spring pushes the coloured flag. Expensive ones also operate a microswitch to alert the building controllers to send a man out with a new cartridge.
    Mike

    * those do have an internal fuse of sorts. Not sure its breaking ability.

Reply
  • On the simple wylex/crabtree types, that indicator window is usually held up against a spring, by the bit of fusewire (*)that evaporates when the SPD goes short circuit, then the spring pushes the coloured flag. Expensive ones also operate a microswitch to alert the building controllers to send a man out with a new cartridge.
    Mike

    * those do have an internal fuse of sorts. Not sure its breaking ability.