What do you put on an EICR when there is no/faulty smoke detectors in a domestic property?

What do you put on an EICR when there is no/faulty smoke detectors in a domestic property?

Parents
  • A little sidebar

    www.fia.uk.com/.../fire-fears-grow-as-million-admit-to-never-testing-smoke-alarms.html

  • That is an interesting and article & indirectly suggests that 80% of fires occur in homes with fire alarms probably because they are pretty common. It is important to balance this with the fact that fires are mercifully rare - most houses will reach demolition and never have seen one, so most of the folk not checking their alarms because it is not very likely, are in a way correct, it is not very likely. (compared to say a car crash or tripping over the stair carpet).

    Even if we disabled  all fire alarms at once, we'd never get back to the  rate we had before they were invented, as we no longer have open fires, or anything like as many people smoking indoors, or worse smoking in bed.. 

    I wonder how much of an up-tick they would consider serious.

    Mike.

  • As a Friday Folly, it would be interesting to see if of all the same people that were surveyed about testing smoke alarms monthly how often they test their RCBO every 6 months.  (Hopefully when they change their clocks for daylight saving)  I suspect fewer people test their RCD in the UK than test their smoke alarm.

    Now this could indeed be masking an issue.  Does the RCD actually work as intended?  

    Eg of fails
    Type AC RCBO in the domestic dwelling being blinded by DC
    Jamed/Fused/seized mechanism
    Unable to re-initialise circuit due to device fault

Reply
  • As a Friday Folly, it would be interesting to see if of all the same people that were surveyed about testing smoke alarms monthly how often they test their RCBO every 6 months.  (Hopefully when they change their clocks for daylight saving)  I suspect fewer people test their RCD in the UK than test their smoke alarm.

    Now this could indeed be masking an issue.  Does the RCD actually work as intended?  

    Eg of fails
    Type AC RCBO in the domestic dwelling being blinded by DC
    Jamed/Fused/seized mechanism
    Unable to re-initialise circuit due to device fault

Children