Metal conduit between two light fittings

Hi all,

we are having a discussion in the office and wanted your thoughts on the subject. If you have a metal conduit fitted between two plastic light fittings, the circuit is wired in singles (including a separate CPC), is there a requirement to earth the metal conduit? 

Parents
  • Only exceptions I can think of if is the circuit isn't normal LV - e.g. SELV or perhaps separated LV, or (very rarely) if the conduit was out of reach (unlikely in uncontrolled environments like normal offices).

       - Andy.

Reply
  • Only exceptions I can think of if is the circuit isn't normal LV - e.g. SELV or perhaps separated LV, or (very rarely) if the conduit was out of reach (unlikely in uncontrolled environments like normal offices).

       - Andy.