Solar PV into load side of RCD

At Section 8.8 in the COP for Grid connected Solar PV systems it clearly indicates that the inverter should not be connected to the load side of any RCD that is shared with other circuits. The note explains the reasons without elaboration.

I am trying to understand how an inverter would continue to supply the fault after the RCD has operated. Is it not a separated circuit at the loss of supply?

 

Parents
  • Regarding the COP requirement is it more to do with if the other downstream circuit experiences a fault and RCD operates then PV is disconnected from upstream network? 

Reply
  • Regarding the COP requirement is it more to do with if the other downstream circuit experiences a fault and RCD operates then PV is disconnected from upstream network? 