Connection of back-upgenerator to TN-C-S domestic installation
Hi All. I'm a medically retired electrician with additional strings to the bow throughout my career. From contracting on commercial electrical installations to building/designing large industrial containerised generators to managing landfill gas generator installations and finishing at building maintenance engineer covering alot of variable skills with HVAC and BMS.
I try to keep the mind busy and do what I can.
Appreciate your viewing my question I'll try to be as descriptive as possible.
My home is TN-C-S supply with no extraneous parts ( water supply is plastic pipe and no gas supply).
Approximately 5 years ago I installed a large metal garage/workshop 7.5m by 4.5m(concrete floor with metal box section frame bolted to the concrete pad)
I supplied the garage with a 6mm armoured  via 30ma RCD and 40amp MCB ,armour being connected to house distribution board and isolated at the garage termination so as not to export the earth as per regulation,I installed 2m deep electrode and additional 1m deep electrode both wired back to garage DB. So in effect garage is on a TT system.
The house distribution boards (8 way mem bs88 and 4 way mem2000 RCD mcb) I want to change out for 1 large regulation DB , one in looking at is MK dual 100amp 30ma isolator with type 2 SPD rest populated with mcb's.
To the nub of my question. I want to install back up generator (7.5kva peak 6.25kva constant)which will be sited out the back of the metal garage( outside garage building not inside)some approx 12m from house. I'll give you my thoughts on what I'm thinking of installation to ensure complete separation from incoming mains supply to remove chance of any back feed especially under fault condition.
1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.
2.Wired back to a 20amp double pole rcbo enclosure in distribution cupboard.
3.From rcbo into a manual 3 pole  transfer switch.
4.The network supply wired the manual 3 pole transfer switch then from transfer switch to new distribution board (dB).
5. The generator chassis will be connected to garage earth electrodes when in use.
6.. 3 pole manual transfer switch? My thinking is to switch L. N. and the earth.
My thinking on this: when mains is in use garage supply has isolated earth DB side connected only  as previously discussed to protect cable/circuit going to garage rest of house still using supplier earth path .
When generator supply is used the whole installation house including garage would be effectively TT system this way no chance of back feed to the supplier network including under fault conditions from my/consumer end giving earthing is also switched at the manual transfer switch, i
Q.1.is this 3 pole manual transfer idea (switching earths) idiotic/unnecessary/ not advisable ?
Q. 2. Should I include a type 1 SPD to the 20amp 30ma generator supply enclosure inside distribution cupboard given large metal shed and lighting strikes ?
Sorry for long winded pre log just trying to ensure you've all the information needed. Would be grateful for your thoughts and indeed advice.
  • I'm not for one moment suggesting we should not consider the intention of the legislation, but the presence of the Double Pole change over switch means this example is NOT source of energy (what we call a 'generator' ;-) ) which may be connected in parallel with a distributor’s network (what we call 'the mains' ).
    I never suggested it was ... it remains true, however, that the arrangement is covered by Regulation 21 of ESQCR (Regulation 22 of ESQCR NI) and I agree in this case Regulation 22 of ESQCR (Regulation 23 of ESQCRNI) would not apply.
  • Hi Dave , valuable contribution, i appreciate your taking the time. I agree interpretation when reading and understanding regs/legislation  can lean/interpreted to making it work for individuals requirements. My intention in raising the questions was to remove my individual bias if you like, have good open discussion with better minds than my own frankly and reach overall consensus. Grateful to all contributions.
  • Hi Mike, what you refer was my initial train of thought.
    Which id replied to gkenyou broadly saying i believe regs in G99/NI and ESQCR didn't apply/out of scope to my installation (back up emergency supply only designed for owners property/ Island mode only as it referred) this was because for the most part they reference "export" ,"paralleling" and syncing and such like onto DNO/grid/network..
    gkenyou, rightly pointed out that they do apply and kindly reference me back on some of them, my intent dismissing them originally wasn't to say i hadn't taken them into consideration before posing the question, more that in the small area i had to consider within them, that my proposed install would be meeting requirements. That said was glad gkenyon did so helped in retracing areas i may have failed to consider.
    Your train of thought seems was similar to my own that once "double pole" "break before make" bypass/change-over was in place conditions has been met and that my generator was no longer a "source or Energy" which had the ability to connect in parallel to dist network
    From that thinking and as below from ESQCR.
    Regulations 26(1) and 26(2) of the ESQCR require the consumer’s installation to be:"...so constructed, installed, protected and used or arranged for use so as to prevent, so far as is reasonably practicable, danger or interference with the distributor’s network or with supplies to  others."
    "Danger and interference", to my thought process , if my generator is operating during a power failure (which majority is due to a line fault) and im connected still to the DNO earth, and potentially my generator/installation could develop a fault and i introduce fault current .......so thoughts then went on to eliminate this why not just switch the earth in the same "break before make" bypass switch.
    Prosumer Electrical Installation 4.1 Earthing
    "An electricity supply company may provide an earth at the point of connection but its primary function is protection of the network upstream from the installation. Under the requirements of the Electricity Supply Quality and Continuity Regulations (ESQCR), the consumer is responsible for ensuring that the installation is satisfactorily earthed"
    My thoughts here when operating in PEI and in grid terms "island mode" ,"consumer to responsible own earthing" , "earthing arrangement using a transfer switching device to facilitate the connection to the earthing arrangement of the local star/mid-point or the local exposed conductive parts" and by using a switched earth to customers own earthing system (in emergency use /island mode) whilst isolated from DNO. regulation is fulfilled "reasonably practicable, danger or interference with the distributor’s network or with supplies to  others." as i am only generating during mains failure tbh 99% time is this is due to a network fault, earth switching would prevent fault current back feed from DNO and indeed if i have a fault when in "grid terms" "island mode" no chance of me introducing earth fault onto DNO grid
    Hopefully a consensus from and by others on what id originally proposed and the correctness of such can either be agreed or indeed rebutted..
  • To further muddy the water in this case when the "domestic client" is also the contractor....
    Yes, I had that in mind too ... nowhere to run and hide?
  • Hi Andy, Thankyou for you help , I've had a lot to mull over last few days .
    If you could indulge me and hopefully offer a little clarity on my way forward.
    1. Install generator behind metal garage outside of the building, with neutral earth link in windings and chassis/engine/alt connected to earth pit electrode (one of the two pits of electrodes linked together currently to garage db for metal garage TT set up from house TN-C-S supply, supply cable earthed at house db isolated at garage).
    2. Install 32amp inlet socket to corner of house to an individual (separate to what will be new db) 20amp rcbo /spd encloser in distribution cupboard.
    3. Then into 2 pole "break before make isolator/bypass" along with DNO supply connecting all earths to MET.
    4. From "break before make isolator/bypass" to new bs7671 compliant db.
    5. supply cable to house inlet will obviously be a temp affair if and when generator is to be used.
    So in normal DNO power usage garage installation is still effectively TT.
    During mains fail and gen hook up (inno over kill for 20amp from generator but was going to use 6mm hi-tuff or the like temp cable about 14m run to house inlet). Meaning in this scenario all earths are linked at MET in house and any fault current would be linked via temp lead to earth electrodes.
    Do you think this sounds better than my original switching earths at bypass so as to isolate from DNO earthing in cases of network fault/mains failure?
    I'm still of the thought that all relevant regulations (reviewed and highlighted) that do apply would allow for switched earth, but appreciate I may be interpreting different to others and if consensus is not to ill go with that.
    Appreciate all your input and advice, p.s don't know how these forum things work will everyone that's contributed see this or do i need to send to them individually . Thanks again.
  • Hi gkenyon, could i ask for your thoughts . Much appreciated.
  • Maybe easier with a diagram. I think what you're suggesting is something like this:
    Which I think is OK generally, but my worry would be if the generator (with it's frame connected to the supplier's PME earthing facility) is within reach of the TT'd workshop (with it's frame/cladding bonded to the TT earth and/or accessible class I items e.g. outdoor lights).
    (Technically I suppose the wording of BS 7671 only demands that simultaneously accessible exposed-conductive-parts are connected to the same earthing system, so perhaps and exposed-conductive-part and a (bonded) extraneous-conductive-part on different systems aren't prohibited, but the laws of physics aren't so discriminating, so maybe good engineering practice would want to treat them the same as far a possible.)
  • p.s don't know how these forum things work will everyone that's contributed see this or do i need to send to them individually
    It's a public forum - everyone sees everything! If you mention someone in particular they likely get a notification as well.
  • lol i get that just didn't know cos they where on thread they'd get notification individually. Thanks