Connection of back-upgenerator to TN-C-S domestic installation
Hi All. I'm a medically retired electrician with additional strings to the bow throughout my career. From contracting on commercial electrical installations to building/designing large industrial containerised generators to managing landfill gas generator installations and finishing at building maintenance engineer covering alot of variable skills with HVAC and BMS.
I try to keep the mind busy and do what I can.
Appreciate your viewing my question I'll try to be as descriptive as possible.
My home is TN-C-S supply with no extraneous parts ( water supply is plastic pipe and no gas supply).
Approximately 5 years ago I installed a large metal garage/workshop 7.5m by 4.5m(concrete floor with metal box section frame bolted to the concrete pad)
I supplied the garage with a 6mm armoured  via 30ma RCD and 40amp MCB ,armour being connected to house distribution board and isolated at the garage termination so as not to export the earth as per regulation,I installed 2m deep electrode and additional 1m deep electrode both wired back to garage DB. So in effect garage is on a TT system.
The house distribution boards (8 way mem bs88 and 4 way mem2000 RCD mcb) I want to change out for 1 large regulation DB , one in looking at is MK dual 100amp 30ma isolator with type 2 SPD rest populated with mcb's.
To the nub of my question. I want to install back up generator (7.5kva peak 6.25kva constant)which will be sited out the back of the metal garage( outside garage building not inside)some approx 12m from house. I'll give you my thoughts on what I'm thinking of installation to ensure complete separation from incoming mains supply to remove chance of any back feed especially under fault condition.
1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.
2.Wired back to a 20amp double pole rcbo enclosure in distribution cupboard.
3.From rcbo into a manual 3 pole  transfer switch.
4.The network supply wired the manual 3 pole transfer switch then from transfer switch to new distribution board (dB).
5. The generator chassis will be connected to garage earth electrodes when in use.
6.. 3 pole manual transfer switch? My thinking is to switch L. N. and the earth.
My thinking on this: when mains is in use garage supply has isolated earth DB side connected only  as previously discussed to protect cable/circuit going to garage rest of house still using supplier earth path .
When generator supply is used the whole installation house including garage would be effectively TT system this way no chance of back feed to the supplier network including under fault conditions from my/consumer end giving earthing is also switched at the manual transfer switch, i
Q.1.is this 3 pole manual transfer idea (switching earths) idiotic/unnecessary/ not advisable ?
Q. 2. Should I include a type 1 SPD to the 20amp 30ma generator supply enclosure inside distribution cupboard given large metal shed and lighting strikes ?
Sorry for long winded pre log just trying to ensure you've all the information needed. Would be grateful for your thoughts and indeed advice.
  • generator (that isn't a generator) doesn't run at high voltage.
    I would perhaps say that the AC side of their generator doesn't run at high voltage, but that's perhaps another debate which is not, perhaps, completed.
  • the OP's generator isn't a generator.  And the OP isn't a generator either, because their generator (that isn't a generator),,,
    And that, ladies and gentlemen, is the sort of thing that happens when you let the legal chaps draft anything technical, and then let politicians edit it. Too many holes.
    What for example if I had an LV generator and stepped it up to HV to run the length of a large farm and then stepped it back down to LV before it was used to supply any loads ?  (I am aware of at least one of these in the UK )
    So it is far more important that this installation is safe for its users, and can not damage  the DNO network, or rely on it when it may not be there for earthing, than agonising over which bit of legislation is or is possibly not appropriate, though it is quite fun.
    Unless the OP refers himself to the police, who probably won't be interested anyway, we'll never know.  The only time such laws are tested in earnest is after there has been a serious accident and then some sort of inquiry, and the trick is to avoid that under all circumstances.
  • Sorry just seen the 'out of loop' query, and yes, the loop I refer to is the loop of L>fault> CPC>NE bond> back to source, it is the only fault path to earth with a lot of amps.
    And as Andy has so well drawn, that fault loop, neither requires nor includes the DNO NE bond when on genset, and if you switch over and redraw it does not include or require  the genset NE bond when switched to mains.
    Casually  speaking the you might say that the unused NE bond is out of (the fault current) loop.
    Apologies for the initial sloppy choice of words, hope the fog is clearing.
    In terms of shocking the DNO you can probably hit it with anything less than 25V forever and the sort of events you would permit normally while ADS operates - so up to perhaps half mains for 0,4 secs or less, that sort of thing. It is not good, and should not occur by design, but in a rare transient fault condition, it is unlikley to kill anyone.
  • Oooh, the earthing 'System'. A real hotch potch of misunderstanding disinformation and confusion.
    We almost always show the live (power), and neutral ('returning power') neatly at the top and middle of our diagrams, and then mark the earthy things as an after thought at the bottom among the notes and other incidentals. A few symbols here and there, but without an real feel for what's going on (until push comes to shove and someone else causes a problem;-)
    It's worth trying to draw out the circuits with the Earth System at the top (core mass of earth at the very top) and then see how well one can represent the earthing and its resistance/impedances at the various places (all those magic values the DNOs claim, and earth rod minimums, etc). The circuit should include representations of the physical current flows so those faulty street lights, neighbours and adjacent sub-station issues can be 'considered'.
    It all gets very interesting once we realise just how 'bad' (as a consistent connection) the general earthy stuff is, and what different folks are expecting from it.  As an aside/excercise; consider if there is any effect from say, deliberately adding an extra earth rod by the house (adjacent to any existing earth bond) and a similar additional earth rod at the garage, and connect the two of them directly together (but independent of any other circuit) with a hefty insulated cable. It's just extraneous, non-contributing, surely? The question is, does it carry any current, whose current, when, who cares?
    It's a rabbit hole, and all the specs/regs don't do a great job of explaining.
    [Now to catch up with the rest of the discussions  See no evil]
  • yes, there are some parts of the supply regs which apply to legal entities who are "generators" as defined in the regs. however, there are other requirements (including regs 21 & 22 of the supply regs and regs 22 & 23 of the statutory rules for Northern Ireland) which apply to any person:
    • reg 21/22: Where a person operates a source of energy as a switched alternative to a distributor’s network, he shall ensure that that source of energy cannot operate in parallel with that network and where the source of energy is part of a low voltage consumer’s installation, that installation shall comply with British Standard Requirements.
    • reg 22/23: (1) Without prejudice to regulation 21[/22], no person shall install or operate a source of energy which may be connected in parallel with a distributor’s network unless he—
      (a) has the necessary and appropriate equipment to prevent danger or interference with that network or with the supply to consumers so far as is reasonably practicable;
      (b) has the necessary and appropriate personnel and procedures to prevent danger so far as is reasonably practicable;
      (c) where the source of energy is part of a low voltage consumer’s installation, complies with British Standard Requirements; and
      (d) agrees specific requirements with the distributor who owns or operates the network.
      (2) Sub-paragraphs (b) and (d) of paragraph (1) shall not apply to a person who installs or operates a source of energy which may be connected in parallel with a distributor’s network provided that sub-paragraphs (a) and (c) of paragraph (1) are complied with; and
      (a) the source of energy does not produce an electrical output exceeding 16 amperes per phase at low voltage;
      (b) the source of energy is configured to disconnect itself electrically from the parallel connection when the distributor’s equipment disconnects the supply of electricity to the person’s installation; and
      (c) the person installing the source of energy ensures that the distributor is advised of the intention to use the source of energy in parallel with the network before, or at the time of, commissioning the source
    you will observe that these key requirements (including preventing danger and complying with the wiring regs when in scope) apply to any person with a source of energy. reg 22/23 is so important that it applies retrospectively, which isn't generally the case when new rules are introduced
    I agree that what matters most is that the installation is safe, but I think that understanding the legislation does matter too. I'm sure that there's something in UK-SPEC about understanding relevant legislative and regulatory frameworks, so you don't have to take my word for it.
    There seems to me to have been some confusion in this discussion about which rules apply where, so I want to avoid people thinking that certain rules don't apply to their installations because they've seen what appears to be a loophole but the parliamentary draughtsman has been smarter than they may have been given credit for. the key rules apply to any person who operates a source of energy
  • you will observe that these key requirements (including preventing danger and complying with the wiring regs when in scope) apply to any person with a source of energy. reg 22/23 is so important that it applies retrospectively, which isn't generally the case when new rules are introduced
    and similarly Regulation 21 (22 in NI) if the generator operates as a switched alternative, this needs to provide safety for those working on the distribution network, and BS 7671 is to be used.
    Interesting with these two Regulations in ESQCR, it is the 'person' who 'operates' the generator (that could be, again, a 'legal person' as an entity), not the installer, who has the duty under the Regulations, and might be proceeded against under the Regulations (unlimited fine I believe).
    However, that would not stop the 'person who operates' being able to take action against an installer if the installer were the designer recommending the change to the electrical installation.
  • I imagine that there's a CDM angle to this, where ultimately the client is responsible for appointing the right people to do the right things
  • I'm not for one moment suggesting we should not consider the intention of the legislation, but the presence of the Double Pole change over switch means this example is NOT source of energy (what we call a 'generator' ;-) ) which may be connected in parallel with a distributor’s network (what we call 'the mains' ).
    Unless you think 'connected in parallel' does not mean electrically in parallel.
    However, failing that first test does not mean that it should not be wired up without due diligence.
    Things that can be configured to synchronise and export power back out and onto the grid are quite a different matter, as in fault states, they have potential to damage both the network and other users equipment, and quite rightly are treated with more rigour.
  • agreed: it's then caught by reg 21/22, which requires a robust change-over and also compliance with the wiring regs
    Agreed, although worth noting further that, where there is a 'domestic Client' (work done for a private homeowner) the Contractor takes on the Client's duties under CDM ...