13A supply to 16A (3.2kW) machine. It works fine, but is it illegal?

Hi,

I'm working with a machine that has a data plate for 3.2kW but this is peak, when all elements are running.  I have it running on a 13A RCD protected supply with no problems, but it has been suggested this is illegal.  I could understand a small machine running on a large supply, but the fact that it draws less current than the data plate surely means it is safe, although maybe running closer to the current limit. 

In service testing regs talk about fusing of circuit to protect, but never the other way round.

Can anyone quote me a reg saying either way?

Parents
  • but it has been suggested this is illegal

    Forgetting BS 7671 for a moment, if any safety incident occurs, which could range from burns to damage to electrical equipment causing a fire or shock, if this is in a workplace, it could be considered as a potential breach of legislation ... i.e. 'illegal'. Worth having a look at, in particular the Electricity at Work Regulations:

    Regulation 5: Strength and capability of electrical equipment

    Regulation 11: Means of protecting from excess current

    In terms of BS 7671, in my opinion, it's not conformant if you are using 13 A accessories, or a 13 A overcurrent protective device, to supply the equipment. Regulation 132.2.2 in particular:

    133.2.2 Current
    Electrical equipment shall be selected with respect to the maximum steady current (rms value for AC) which it has to carry in normal service and with respect to the current likely to be carried in abnormal conditions and the period (e.g. operating time of protective devices, if any) during which it may be expected to flow.

    If you are supplying through a BS 1363 series plug and socket-outlet combination, or any type of connection unit to BS 1363-4, it's worth remembering that the likelihood of damage from overheating, particularly around the fuse, increases as you go above 13 A load current. BS 1362 fuses are required to have a maximum power dissipation of 1 W at their rated current. A 'calibrated test link', that is designed to dissipate 1 W, is used in temperature rise tests, during type testing in the relevant parts of the BS 1363 series of standards.In addition, the  conditions of use in BS 1363-series should be considered.

    For example, it is common to see BS 1363 plugs overheating around the fuse, and externally the line pin  of the plug (which is close to the fuse) if used with welding equipment with peak input current of 14-15 A, even if this is short-term.

    So, what to do?

    If there is no evidence of overheating at the moment, recommend any 13 A equipment is checked regularly (if possible, by users) for signs of overheating.

    Recommend, if possible, connection by an appropriate-rated isolator, connection unit, or socket-outlet ... if a workplace, for example, BS EN 60309-2 or BS EN 60309-4 socket-outlet ('commando socket') could be used. Even if this requires a new circuit, it's probably still going to be in the ballpark of 'reasonably practicable' ?

  • Thankyou so much for your prompt answer!