13A supply to 16A (3.2kW) machine. It works fine, but is it illegal?

Hi,

I'm working with a machine that has a data plate for 3.2kW but this is peak, when all elements are running.  I have it running on a 13A RCD protected supply with no problems, but it has been suggested this is illegal.  I could understand a small machine running on a large supply, but the fact that it draws less current than the data plate surely means it is safe, although maybe running closer to the current limit. 

In service testing regs talk about fusing of circuit to protect, but never the other way round.

Can anyone quote me a reg saying either way?

Parents
  • 13A supply to a 16A machine (kitchen cooker could be an example)

    Points to consider

    A dedicated circuit rated appropriately with a 4mm2 or 6mm2 CSA dependent on VD (Volt Drop) and clipping reference

    A dedicated 16a or 20amp RCBO type A or higher certainly not type AC

    Use a 16amp commando rather than a 13amp BS 1363 plug

    Case in point for when a 16A unit is served by a 13amp would an immersion heater in boiler cylinder or electric shower the FCU generally tend to show thermal damage after prolonged use.  

    Now the question is do you need a regulation or the use of engineering judgement?  Other points to consider would be the energy efficiency of an install if it is operating in the contingency zone. As we know a 13amp plugtop fuse will run at 16amp comfortably for hours.   The heat of the cable will make it less energy efficient.  The risk potential for an incident or fire are greatly increased.

Reply
  • 13A supply to a 16A machine (kitchen cooker could be an example)

    Points to consider

    A dedicated circuit rated appropriately with a 4mm2 or 6mm2 CSA dependent on VD (Volt Drop) and clipping reference

    A dedicated 16a or 20amp RCBO type A or higher certainly not type AC

    Use a 16amp commando rather than a 13amp BS 1363 plug

    Case in point for when a 16A unit is served by a 13amp would an immersion heater in boiler cylinder or electric shower the FCU generally tend to show thermal damage after prolonged use.  

    Now the question is do you need a regulation or the use of engineering judgement?  Other points to consider would be the energy efficiency of an install if it is operating in the contingency zone. As we know a 13amp plugtop fuse will run at 16amp comfortably for hours.   The heat of the cable will make it less energy efficient.  The risk potential for an incident or fire are greatly increased.

Children
  • As we know a 13amp plugtop fuse will run at 16amp comfortably for hours.   

    The fuse might not operate ... but that doesn't mean the temperature in the fuse holder is classed as 'comfortable'. In addition, surface temperatures of equipment housing the fuse may well exceed the limits of Table 42.1 of BS 7671 and/or the product standard (see Regulation 423.1).