13A supply to 16A (3.2kW) machine. It works fine, but is it illegal?

Hi,

I'm working with a machine that has a data plate for 3.2kW but this is peak, when all elements are running.  I have it running on a 13A RCD protected supply with no problems, but it has been suggested this is illegal.  I could understand a small machine running on a large supply, but the fact that it draws less current than the data plate surely means it is safe, although maybe running closer to the current limit. 

In service testing regs talk about fusing of circuit to protect, but never the other way round.

Can anyone quote me a reg saying either way?

Parents
  • In my view, it depends on for how long the overcurrent could reasonably persist.

    A few minutes, once a day whilst warming up, almost certainly OK. (the old fashioned "three bar" 3kw radiant heaters were allowed on 13 amp plugs, If starting from cold they used 16 amps or more for a couple of minutes, and no one worried)

    For hours at a time, if the equipment is in heavy or repetitive use, with a high mains voltage of 250 volts. Rather concerning. If this is the case, I would urge use of a 16 amp ceeform outlet, connected to a 16 amp MCB, via at least 2.5mm cable.

Reply
  • In my view, it depends on for how long the overcurrent could reasonably persist.

    A few minutes, once a day whilst warming up, almost certainly OK. (the old fashioned "three bar" 3kw radiant heaters were allowed on 13 amp plugs, If starting from cold they used 16 amps or more for a couple of minutes, and no one worried)

    For hours at a time, if the equipment is in heavy or repetitive use, with a high mains voltage of 250 volts. Rather concerning. If this is the case, I would urge use of a 16 amp ceeform outlet, connected to a 16 amp MCB, via at least 2.5mm cable.