13A supply to 16A (3.2kW) machine. It works fine, but is it illegal?

Hi,

I'm working with a machine that has a data plate for 3.2kW but this is peak, when all elements are running.  I have it running on a 13A RCD protected supply with no problems, but it has been suggested this is illegal.  I could understand a small machine running on a large supply, but the fact that it draws less current than the data plate surely means it is safe, although maybe running closer to the current limit. 

In service testing regs talk about fusing of circuit to protect, but never the other way round.

Can anyone quote me a reg saying either way?

Parents
  • Not "illegal", but potentially unwise.

    What is the machine, and for how long is it typically used?

  • Agree - its not illegal in the sense the police will break down your door.

    Nor is it against the wiring regs. 

    But it may be the sort of thing that insurance companies might decide to point to if there is a fire, to justify not paying in full. In a place of work it may be seen as endangering the workforce.

    Things like ovens and hot plates are a classic for this  - where the sum of all the heaters greatly exceeds the supply rating, but so long the situation can be avoided where it is all switched on at once for a cold start, in practice it runs without issues.

    note that 13A *230V is 2.99kW and 13A * 240V is 3.12kW.  Look hard at that plate - what is the voltage is has been tested at ?

    3.2kW is not really a full fat 16A - that is much closer to 3.7 (230V) or 3.8kW (240V).

    You may be overloading things, but not by an amount likely to be any more dangerous than full load. And  I say it like that because there are plenty of designs of 13A plugs, and even more 13A extension leads, that actually run very warm at 13A and don't take much in the way of restricted ventilation or a warmer than normal  environment, to tip them over the edge at currents below the nominal  13A anyway.

    This example of a 13A plug and socket were on a ~ 3kW heated catering service counter - the fuse did not blow, but as you can see, it ran 'really quite warm'. My warning is that there really is not a lot of slack in some examples of nominally '13A' rated hardware.

    Mike.

  • its not illegal in the sense the police will break down your door.

    That might not be the case if someone is seriously hurt, or worse, unalived, during a resulting conflagration !!