Definition of 'electrical installation' and requirement to upgrade existing to current regs?
Hi there
Have found an old damaged 30A JB on a ring final under the floorboards, which I was going to replace - although it spurs to a 2G socket, from which three further sockets are spurred. Obvs you can't have a spur off a spur without a fused connection (which this doesn't have), but is there a specific requirement to upgrade the existing wiring either (a) once the 'non compliant' aspect has been found or (b) as a result of the intervention in the circuit (i.e. does the replacement of the broken JB automatically mean that the spur+spur issue has to be rectified also?).
The wiring is not that old (blue neutral plus other evidence suggests probs 15 - 20-ish years max) so not sure if it would have even been compliant with the regs at the time - but would be pretty difficult to either bring the spurs back to the ring or fit a fused connection due to the location / buried cables etc etc. Might be possible to split the ring into two radials etc (which would probably have incidental benefits) but obvs this is an order of magnitude more substantive work-wise than replacing the damaged JB...
Cheers
  • [Surely] It's that 4-bar electric fire (4kW) with a 0-4 switch (if they exist) that would be an equipment load that should 'never' be load limited by the fuse such that the user doesn't accidentally use the "4 setting" on a circuit that's not designed for it.   Or something like that.
  •  Agreed ... one could say what's the difference between the n-bar fire with n switches, and n 1-bar fires each with a plug on its own (hence the socket-outlet circuit link).
  • I think, though, there's a difference between the "kitchen sockets" vs the "upstairs sockets" when taking this into account ... clearly one usually has more propensity for accidental overload due to anticipated loads involved.
    Which one?
    I doubt that electric heaters are used as much in kitchens as bedrooms.
    Moreover,
    the other big load devices (hob, oven, washing machine) are on separate rings or radials
    So in this case, the dishwasher may be the biggest load in the kitchen, but it will not be heating water for long.
  • I believe that one 'plans' the expected/typical value of n (number of sockets) for the n single bar fires and ensures that the circuit's cables are capable of that level of current.
    So in that sense the trip is for 'fault' detection, and that normally the user would not have overloaded the circuit.
    The user would have to work hard to create the problem, while in an N+1 way switch case it's easy for a user slip-up to select the overload case warned about in the extract.
    A good read is Reason's "Human Error" book to see the distinction between slips, lapses and mistakes and their different protection/safety approaches.
  • Portable electric heaters with a single phase loading of more than 3Kw are very rare. In many years of experience I have seen just one !
    It has 4 radiant elements, each of 750 watts, and 3 settings of convector heating with a maximum output of 3Kw, so a total of just over 6Kw, allowing for the improbable number of 60 watt lamps in the decorative fuel effect. It remains in use, and is on a dedicated 30 amp circuit, with final connection via a 32 amp  ceeform plug.
  • True.
    I was suggesting a hopefully easy to grasp hypothetical situation to help give an example that could help with understanding the 'rule' about fuses and circuit breakers for control of 'stupid' [aka uniformed] users.
    They weren't that rare in the 1970s (3-bar fire) ... probably a hang-over from the 1960s ... but since the move towards, and later achievement of, harmonization, agreed ...
    Which one?
    Moreover,
    Any starting point could be considered an assumption, because the socket-outlets could be used for any purpose by any "ordinary person", but generally, perhaps the kitchen given the "usual loads" plus any "odd loads selected by any ordinary person".
    This discussion proves that there is no "guarantee of safety", only a "likelihood of safety" that's possible with an electrical installation - the same holds true for discussions about protection against electric shock.
  • Any starting point could be considered an assumption, because the socket-outlets could be used for any purpose by any "ordinary person", but generally, perhaps the kitchen given the "usual loads" plus any "odd loads selected by any ordinary person".
    And of course, different households do things differently, so what suits the current occupier may not suit the next.
  • Spurs from spurs, are quite common in practice (go back far enough and two single sockets where permitted on a spur, undoubtedly many of those singles got replaced by doubles over the course of time). Not to mention the usual total botches. The worst I came across was most of the kitchen sockets fed from a 4mm or 6mm cable (lollipop style) - presumably originally the cooker circuit but made redundant when the hob was changed to gas - but then it looks like the old cooker fuseway was pinched for a new shower, so the old cooker cable was redirected into the back of a convenient socket ... which happened to be on a spur. So you had in effect an entire kitchen, including a 2kW oven, washing machine and all the usual kitchen appliances, plus the socket usually used for the ironing, all on one 2.5mm2 cable. It had been like that for years apparently - but had it burned the house down? was it frazzled to a crisp? was it looking a bit distressed? not at all - it all looked fine. (it did get changed all the same though). Has anyone else seen a domestic spur cable looking distressed from overload?