Hi,
I am trying to confirm a point.
as long as we meet the max disconnection time (let say 0.4s for a TN system) . for a small power circuit,
Can we ignore the Max Zs requirement ?
Example
Small power radial circuit ,20A RCBO 30mA , type A C curve,
RCD trip time is 20ms
but, max Zs is higher than it should be to Overload trip before 0.4s (lets say Max allowed Zs is 1.09 but the measured is 1.40)
Can we override the 0.4s overload tripping requirement as its already being met with RCD protection of the RCBO ? i.e. as it trips at 20ms anyway so it meets the 0.4s requirement.
Or is this a subjective matter?
Thank you all in advance.