TN system - Max Zs Vs tripping time in the Presence of RCD protection

Hi, 
I am trying to confirm a point. 

as long as we meet the max disconnection time (let say 0.4s for a TN system) . for a small power circuit, 
Can we ignore the Max Zs requirement ? 

Example 
Small power  radial circuit ,20A RCBO 30mA , type A C curve, 
RCD trip time is 20ms 

but, max Zs is higher than it should be to Overload trip before 0.4s (lets say Max allowed  Zs is 1.09 but the measured is 1.40)

Can we override the 0.4s overload tripping requirement as its already being met with RCD protection of the RCBO ? i.e. as it trips at 20ms anyway so it meets the 0.4s requirement. 

Or is this a subjective matter? 

Thank you all in advance. 

Parents
  • You can’t “ignore Zs,” but on a TN system you may rely on the RCD part of an RCBO for fault protection (ADS) instead of the MCB curve—if you verify to the RCD criteria rather than the MCB tables. In BS 7671 this is allowed (TN: Reg 411.4.5 / 411.4.204); use Table 41.5 (RCD method) instead of Tables 41.2–41.4 (MCB method). electrical.theiet.org+1

    What that means for your example (20 A Type C RCBO, 30 mA):

    • Your measured Zs = 1.40 Ω is higher than the MCB-only limit (e.g., 1.09 Ω), so it fails the MCB route.

    • But for an RCD, the criterion is essentially Zs ≤ 50 V / IΔn → for 30 mA, ≈ 1667 Ω (see Table 41.5). Your 1.40 Ω passes easily, so ADS is met—provided the RCD disconnects within 0.4 s for final circuits ≤ 32 A (which your 20 ms test already shows). electrical.theiet.orgProfessional Electrician

    Don’t forget:

    • Overcurrent (overload/short-circuit) protection must still be satisfied by the RCBO’s overcurrent part—RCDs don’t protect L-N faults. electrical.theiet.org

    Bottom line:
    Yes—you can comply via the RCD route on TN. Verify Table 41.5 (RCD) + 0.4 s disconnection, and keep the RCBO’s overcurrent protection in place. electrical.theiet.org+

  • Bottom line:
    Yes—you can comply via the RCD route on TN. Verify Table 41.5 (RCD) + 0.4 s disconnection, and keep the RCBO’s overcurrent protection in place. electrical.theiet.org+

    And, don't forget, if you use a voltage-dependent RCD/RCBO with E2 or E3 marking, check with the manufacturer regarding suitability for ADS ("indirect contact").