Fail EICR because of partial RCD protection

Hi Everyone,

I just had an EICR inspection, and in the picture you can see my CU, which shows the lighting circuits on the right side without any RCD protection. My house was built in 2000–2001. In my previous EICR inspection (2021), this was recorded as a C3 (partial RCD protection), but the new inspector today said I must replace the CU, otherwise it’s a fail of EICR (C2).

He told me that under the new regulations, the lighting circuits must be RCD protected — is that correct? I’m confused about whether older houses need to meet the latest standards, because if so, wouldn’t every landlord with an older property have to replace their CU? I thought new regulations only apply to new installations from the time they are introduced.

Where can I find the official guidance on this? The inspector only showed me some random Google searches, which didn’t look very reliable.

For context: the plastic CU is on the ground floor, and although it’s around 25 years old, it’s fully functional and looks almost new. All bathrooms are on the first floor, with a ceiling height of about 2.4m.

Do I really need to replace my CU? The quote I’ve been given is around £640 for a CU replacement include a 5-year EICR.

Any advice would be greatly appreciated.

Parents
  • I’m confused about whether older houses need to meet the latest standards, because if so, wouldn’t every landlord with an older property have to replace their CU?

    Potentially yes. Have you read the other recent thread about failing an EICR for lack of RCD protection?

    The system does not quite work this way, but IMHO, it is inappropriate to keep issuing C3 for the same item. In a sense the inspector is saying, "I shall pass you today, but please get it fixed before the next inspection."

    Parliament, in its wisdom, has decided that privately let properties must have a safe electrical installation.

    Frankly, £640 including the EICR is very reasonable. Deduct the cost of the EICR, deduct income tax, and it does not amount to much for 5 years' peace of mind. Look at it as an investment, just like replacing an outdated kitchen appliance.

    There is one alternative solution, which I do not recommend, but the immersion and garage circuits probably do not need RCD protection, so the CU could be rearranged.

  • but the immersion and garage circuits probably do not need RCD protection

    Unless they're wired in T&E concealed in a wall <50mm deep ... which perhaps likely?

       - Andy.

  • Fair comment!

  • It is what at the time was known as 'split load' or 'split board'.

    The  other thing that would quite likely raise hackles now is it being a plastic bodied CU.

    Is this the only non compliance with the whole installation or are there others ?

    Another ugly fix might be to accquire and install a second RCD beside or  place of the main switch forming 2 RCD protected groups that may need some lighting circuits to share to make room.

     But again its a sticking plaster solution, longer term the whole CU will need to change to meet current regs. I suggest getting one with more ways so there is room for the likely upcoming solar power heat pump etc that will be needed in the coming decades.

    Yes. in the modern world of domestic consumer units they seem to last about 25 years - not due to technical failure,  usually, just to the onward march of the no and type of things folk plug in.  ;-)

    It used to be longer, in the early 1970s our predecessors  were taking out boards installed in the 1930s.

    Mike.

Reply
  • It is what at the time was known as 'split load' or 'split board'.

    The  other thing that would quite likely raise hackles now is it being a plastic bodied CU.

    Is this the only non compliance with the whole installation or are there others ?

    Another ugly fix might be to accquire and install a second RCD beside or  place of the main switch forming 2 RCD protected groups that may need some lighting circuits to share to make room.

     But again its a sticking plaster solution, longer term the whole CU will need to change to meet current regs. I suggest getting one with more ways so there is room for the likely upcoming solar power heat pump etc that will be needed in the coming decades.

    Yes. in the modern world of domestic consumer units they seem to last about 25 years - not due to technical failure,  usually, just to the onward march of the no and type of things folk plug in.  ;-)

    It used to be longer, in the early 1970s our predecessors  were taking out boards installed in the 1930s.

    Mike.