Protective Earth in a 710 medical location with ELV & PoE circuits

Is there a requirement to earth back boxes and/ or metal plates in a medical location when the wiring system is ELV or PoE (normally rated at 24vDC)?

Looking at 414.4.4 states exposed parts of SELV circuit shall not be connected to earth. 

Does this apply to all ELV?

The system will be used in all medical locations

Thanks for any help

Parents
  • Looking at 414.4.4 states exposed parts of SELV circuit shall not be connected to earth. 

    Does this apply to all ELV?

    No - it's a speciality of SELV to keep the circuit Separated (hence the initial S). With PELV and FELV there's no such limitation (but if you do so there's an additional risk of importing a fault voltage from elsewhere - hence SELV is often preferred in some situations)

    As I read 710.411.7, FELV isn't permitted, and 710.414.4.1. seems to ask for exposed-conductive-parts of PELV systems to be connected to protective conductor.

    Whether a back box or metal faceplate constitutes an exposed-conductive-part may depend on the detail of the situation - i.e. whether it's credible that a breakdown of basic insulation or a loose wire could result in the part coming into contact with a live conductor. A lot of RJ45 systems have a plastic module with punch-down terminations that leave a minimal amount of basic insulation (or potentially free wire) exposed after the end of the cable sheath - so I could see a point of view that it might not be.

       - Andy.

Reply
  • Looking at 414.4.4 states exposed parts of SELV circuit shall not be connected to earth. 

    Does this apply to all ELV?

    No - it's a speciality of SELV to keep the circuit Separated (hence the initial S). With PELV and FELV there's no such limitation (but if you do so there's an additional risk of importing a fault voltage from elsewhere - hence SELV is often preferred in some situations)

    As I read 710.411.7, FELV isn't permitted, and 710.414.4.1. seems to ask for exposed-conductive-parts of PELV systems to be connected to protective conductor.

    Whether a back box or metal faceplate constitutes an exposed-conductive-part may depend on the detail of the situation - i.e. whether it's credible that a breakdown of basic insulation or a loose wire could result in the part coming into contact with a live conductor. A lot of RJ45 systems have a plastic module with punch-down terminations that leave a minimal amount of basic insulation (or potentially free wire) exposed after the end of the cable sheath - so I could see a point of view that it might not be.

       - Andy.