Can any meaningful conclusion from a safety perspective be extrapolated from taking such readings? This one taken on tails supplying a rambling installation circa 30 years old, perhaps +1000 outlets of various types. Large plant room, air handling system, hundreds of light points and a fair amount of office equipment all in operation. Load approx 70A per phase. I am not suggesting there is an equivalence with insulation resistance testing but given that IR testing would be close to impossible in such premises, is it at least an effort in that direction? When carried out at individual distribution boards, values ranged from 4 to 7mA. I guess the issue is.....so what?