Not sure I fully agree with Wiring Matters > Years > 2025 > 107 - September 2025

electrical.theiet.org/.../

Personally I think Rotary Isolator would be far better than 20 amp Double-pole switch shown Fig 2 as this allows for isolation and LockOff/LockOut

The cost of the Rotary Isolator is still quite low see URL below.  (Other brands and other Wholesalers are available).


www.superlecdirect.com/.../



As always please be polite and respectful in this purely academic debate.





Come on everybody let’s help inspire the future

  • Rotary Isolator would be far better than 20 amp Double-pole switch

    I'm not sure. Part of the role of that device is to provide functional switching for the end users - many ordinary people will find a rotary isolator much harder to operate than a plate switch - especially the elderly or infirm - a twisting action is much more difficult for those with arthritic fingers for example - and many rotary isolators are very stiff. I've also yet to see a rotary isolator with a neon indicator (or LED equivalent) built-in - again a useful feature for domestic users to confirm that the immersion is actually getting power (rather than only discovering an hour or two later that the bathwater is still stone cold, because the forgotten other switch in the kitchen is still in the off position).

      - Andy.

  • Further ... BS EN 60335 series permits the load current of a heating element at nominal voltage to be 10 % more than the rating plate rating ... this pushes the maximum up to 14.50 A !!

    When we add the increased temperature in the airing cupboard, I think we are well above "reasonable tolerance" for the poor FCU.

    14.5A is only 11.5% over the 13A nominal, or 24% in terms of I^2R heating, in engineering terms that is not that a big difference compared to nominal, particularly for a situation involving the combination of two pieces of equipment with the same nominal ratings!

    Temperatures inside the airing cupboard are not untypical for parts of domestic properties - airing cupboards, boiler cupboards, attics in summer, particularly given that FCUs are used for supply of higher powered heat generating loads -  immersion heaters, storage heaters, heat-producing equipment etc.

    I rather think to problem lies with insufficient current carrying capability of the accessories, there should be a greater margin between the declared nominal current rating and its actual design and test ratings, a bigger safety margin, to cover these tolerances in voltage, load current, ambient conditions and age-related degradation.

    It strikes me as poor practice to have standards with so little margin between the nominal rating and the design/test rating of the accessory such that equipment with the same nominal current rating in typical conditions can take the accessory to the limit or beyond its capability. This then requiring numerous complex caveats and adjustments, to handle relatively typical domestic scenarios, to address what is basically an inadequacy in the standards for the accessory itself. 

    For example, if an accessory with a nominal 13A rating had a 50% safety margin for I^2 heating, it would be designed and tested at 15.9A, for a 100% margin that would be 18.4A. 

  • In the case if a plug, if rated for 13A and your test current is 14A, so +7.7% in current, or +16% in terms of I^2R heating, that's not much of a safety margin to cover, as you mention, effects from degradation - fuse spring pressure, contact oxidation etc all of which will increase heating above that of a newly manufactured plug/socket/accessory.

    A subtlety that must not be forgotten, is that there are TWO tolerances to take into account that affect current and hence temperature rise.

    The first is the supply and therefore utilization voltage, which can increase to + 10 % of nominal. So, if the nominal current is 11.98 A for a 240 V rated 3 kW heating element, the current at 253 V is 13.18 A ... and I agree that this is covered for in the testing in BS 1363 series.

    Further ... BS EN 60335 series permits the load current of a heating element at nominal voltage to be 10 % more than the rating plate rating ... this pushes the maximum up to 14.50 A !!

    When we add the increased temperature in the airing cupboard, I think we are well above "reasonable tolerance" for the poor FCU.

    Similarly, for a 230 V rated 3 kW element, we have 13.04 A at 230 V (arguably still OK really), 14.34 A with voltage tolerance (now getting a little worrying), and 15.78 A when considering the tolerance permitted by BS EN 60335 series, which again is now getting worryingly high.

    In 2025 we should not be having to discuss topics like whether a 13A load can be used with a 13A accessory in a common household application, it should just work and work safely.

    There is certainly a question why BS EN 60335 series permits 10 % more current (or power) than the rating plate value at nominal voltage, rather than having a requirement that the rating plate current (or power) at nominal voltage should not exceed the rating plate value.

    Combine that with the rather generous (to the manufacturers) allowance of a +52.5 K temperature rise, so in normal 20 deg C ambient conditions allowing a touch temperature of 72.5 deg C, already at a level which causes burns to human skin. There's not a lot of margin to begin with and that's with newly manufactured devices.

    If the surface temperature is too far above 70 deg C, the temperature of the terminals is likely to be above 70 deg C ... not good for PVC, and we do see conductor insulation damage at accessories that have been overloaded.

  • yes, well it is a very different country - my wife has family out there, and it is certainly true to say that the attitude to safety, standardisation, and the rules based world generally, are all very different. 

    But, there are not enough accidents to justify a change of direction. Folk are used to looking out for themselves and things being lethal, and tend to be far more careful that their European counterparts. It is interesting to wonder if in fact we would be safer without some of our H and S culture?

    Mike.

  • Are you suggesting that BS136x possibly needs an update or a revision 2?

    It is certainly an argument that could be made. At the moment there is no easy way to differentiate from a cheap as chips part  made with tin-can grade contact springs in an expensive looking package, and something that actually has some metal and some means of sweating off the heat where it is needed to do so.

    I'd also not be against allowing something more the like the  BS646 fuse - as found in lamp dimmers, some shaver adaptors, clocks an so on as these run considerably cooler, as a way to indicate  connectors that are not really up to the full fat 13A. I'm aware the breaking BS 646 PSSC is 1000A rather than the 6kA of the BS 1362 - but behind a 32A breaker that usually opens before or at the same time as the fuse in the plug, the breaking energy point is a bit moot- there is always an upstream device that limits the energy let through to a safe level.

    Mike

  • so in normal 20 deg C ambient conditions allowing a touch temperature of 72.5 deg C, already at a level which causes burns to human skin

    Well, I think that if you wanted to pull out the plug (in an emergency?) you would let go rather sharpish and not get burned. My interpretation of the standard was that the BS wallahs are more concerned about frying cables than consumers.

  • As with all standards, BS 1363 specifies a set of limits. So if a plug (etc.) experiences a greater temperature rise than 52 K, it has failed the type test.

    Equally important to the limits, are the test conditions and the factor by which they exceed nominal ratings, to provide that safety margin for when the equipment is in use and suffering some typical, in-use degradation.

    In the case if a plug, if rated for 13A and your test current is 14A, so +7.7% in current, or +16% in terms of I^2R heating, that's not much of a safety margin to cover, as you mention, effects from degradation - fuse spring pressure, contact oxidation etc all of which will increase heating above that of a newly manufactured plug/socket/accessory.

    Combine that with the rather generous (to the manufacturers) allowance of a +52.5 K temperature rise, so in normal 20 deg C ambient conditions allowing a touch temperature of 72.5 deg C, already at a level which causes burns to human skin. There's not a lot of margin to begin with and that's with newly manufactured devices.

    For me, its interesting when you compare the approach in Electrical engineering, to other branches of engineering like mechanical and civil engineering, where much bigger factors of safety are typical, and indeed necessary. 

  • In 2025 we should not be having to discuss topics like whether a 13A load can be used with a 13A accessory in a common household application, it should just work and work safely.

    I entirely agree.

    In my opinion the set of BS136x standards need thoroughly revising to introduce a greater factor of safety in the design of plugs, sockets, accessories

    Now I don't agree.

    As with all standards, BS 1363 specifies a set of limits. So if a plug (etc.) experiences a greater temperature rise than 52 K, it has failed the type test.

    I suspect that the better quality BS 1363 devices will barely get warm.

    As Graham has pointed out, the fuse itself will heat up, but the pins have a considerably higher CSA. Granted the conductivity of brass is only about half of that of copper, but I cannot see their contributing much to any warming.

    It seems to me that the fuse holder is probably the weakest link on the basis that the metal is relatively thin, it relies on spring pressure alone, and oxidization could increase the resistance.

  • Brazilians

    Here are a couple of Brasilian electrical adapters which just happen to live in a desk drawer.

    As you can see, the larger one, which can accommodate three different types of plug (but not all at the same time), is rated at 20 A/250 V for the largest pins, so what have we got to worry about?

  • Personally I think Rotary Isolator would be far better than 20 amp Double-pole switch shown Fig 2 as this allows for isolation and LockOff/LockOut

    Should we also replace light switches with rotary isolators?  I have replaced many lamps over the years, but have never yet needed to change the immersion heater.