heat pumps and dual RCD boards new install

we have come across  heat pumps on type A dual (RCD) Residual Current Device boards.

BS7671 does not seem to saying anything on heat pumps, the heat pumps seem to have variable frequency drives.

is this a danger considering blinding may now mean half the property could have a blinded rcd and therefore no additional protection?

would it be reasonable to expect heat pumps to have its own double pole type B HP rcd ,will BS7671 be ammended to include what is likely to become a bigger problem as more are fitted?

Parents
  • with a minimum trigger point of 150mA above 1kHz.

    I'm in the process of fitting a heat pump at the moment - and the manufacturer's instructions say something very similar. They do however note that an RCD is only require where installation conditions require one - so on a TN system with no concealed (or armoured) cables, I reckon I'll be OK without one.

    will BS7671 be ammended to include what is likely to become a bigger problem as more are fitted

    I'm not sure BS 7671 needs an amendment - the problem is not unique to heat pumps, and it's possible not all heat pumps will have this issue. We're already obliged to follow manufacturer's instructions - so that should cover it.

       - Andy. 

  • Once the people at the IET and BSI realise that these are metal boxes placed outside, expect ever more elaborate and impossible to comply with rules, like with EV chargers.