Could someone clarify whether a 100mA/300mA upstream RCD is required for an on-street TT EV installation, where all outgoing circuits are 30mA protected within the feeder pillar DB, also if the outcome is different for a metal or GRP feeder pillar?
BS7671 Reg 531.3.5.3.1, and the Code of Practice for EVCE 'On-street', Section 7.4.2.3 both state that an upstream RCD is required, but this seems to be a very contentious among installers.
There are situations described in the OSG where an upstream RCD can be omitted where certain conditions are met, insulated cable entry gland, meter tails of reinforced or double insulation, secured throughout their length to arrest movement etc.
However, special locations are outside the scope of the OSG and I'm wondering if this is where the different opinion originate.