odd voltages detected on lighting circuit
goodly morrow
all lights working fine -  no 'dim' or not on etc
a three-wire Zs test at a two lighting points on a circuit  ,  indicated  ~115V.
a voltage tester then indicated:
L-N ~240 V   L-CPC ~90 V   N-CPC  ~115 V    (TN-C-S supply .. other circuits seemingly fine)
what might the issue be do you think with the voltages 'divided up' like that ?
thank you
  • As the LN voltage is OK, and the CPC is wobbling about between L-N, my money would be on a poor connection in the path between the MET and the point at the fitting you are measuring as the earth .
    The exact voltages will be determined  by the  balance of things connected acting as a  voltage divider with two capacitors one LE and one NE - that could be a mix of the natural cacitaance of the wire and or the filter capacitors of any LED drivers that are connected.
    Another clue would be that if you connected a moderate load or even a small capacitor accross that 115V it will probably collapse away to a low value.
    The 'make or break' test of that theory will be a wander lead R2 test to the same point.
    let us know what you find.
    regards
  • thanks Mike.
  • your expectation proved, Mike.  Thank you for your input.
    When I picked through this (attached(  lurking in the loft under the insulation and sorted it ... all was well.
  • Ah yes, the use of the fabric of the building as the enclosure.There must be loads like that dotted about. Nicely found... I presume there is now a wagobox or something.. Still apart from that no signs of fire or mice or anything so that's a plus.
    stirs memories of a similar quality set up where I unknowingly stepped on a ceramic screwit and broke so the wire end goes into the sole of the footwear and the foot..
  • "...I presume there is now a wagobox or something..."  -  no one [on here at least] walks away from something like that without properly sorting it I hope   :-)  Thanks again.