Power cable connection on a mobile installation to External equipment using a MIL-DTL-38999 connector.
So I've inherited a a mobile installation project. The power cable connection on to External control equipment uses a dedicated port with a MIL-DTL-38999 connector.
The inrush when the charging system is engaged trips the RCD when it is set to 30mA. My predecessor determined that the connection is not classified as a socket and increased the RCD trip current to 300mA.
Given that it uses the 38999 connectors and it is solely dedicated to the dismounted control systems that form part of the system is this a valid assessment?
  • Be aware that there are significant relaxations of the machinery directive, & it is completely dis-applied for fairground, police or military equipment, or several kinds of vehicle, though generally not otherwise normal equipment that just happens to be mounted on a vehicle.
    quoting the 2023 version.
    2.  This Regulation does not apply to:
    (a)   safety components that are intended to be used as spare parts to replace identical components and are supplied by the manufacturer of the original machinery, related product or partly completed machinery;
    (b) specific equipment for use in fairgrounds or amusement parks;
    (c) machinery and related products specially designed for use within or used in a nuclear installation and whose conformity with this Regulation may undermine the nuclear safety of that installation;
    (d) weapons, including firearms;
    (e) means of transport by air, on water and on rail networks except for machinery mounted on those means of transport;
    (f) aeronautical products, parts and equipment that fall within the scope of Regulation (EU) 2018/1139 of the European Parliament and of the Council ( 1 ) and the definition of machinery under this Regulation, insofar as Regulation (EU) 2018/1139 covers the relevant essential health and safety requirements set out in this Regulation;
    (g) motor vehicles and their trailers, as well as systems, components, separate technical units, parts and equipment designed and constructed for such vehicles, which fall within the scope of Regulation (EU) 2018/858, except for machinery mounted on those vehicles;
    (h) two- or three-wheel vehicles and quadricycles, as well as systems, components, separate technical units, parts and equipment designed and constructed for such vehicles, that fall within the scope of Regulation (EU) No 168/2013, except for machinery mounted on those vehicles;
    (i)  agricultural and forestry tractors, as well as systems, components, separate technical units, parts and equipment designed and  constructed for such tractors, that fall within the scope of Regulation (EU) No 167/2013, except for machinery mounted on those tractors;
    (k) seagoing vessels and mobile offshore units and machinery installed on board such vessels or units;
    (l) machinery or related products specially designed and constructed for military or police purposes;
    (m) machinery or related products specially designed and constructed for research purposes for temporary use in laboratories;
    (n) mine winding gear;
    (o) machinery or related products intended to move performers during artistic performances;
    (p) the following electrical and electronic products, insofar as they fall within the scope of Directive 2014/35/EU or of Directive 2014/53/EU:
      (i) household appliances intended for domestic use which are not electrically operated furniture;
      (ii) audio and video equipment;
      (iii) information technology equipment;
      (iv) ordinary office machinery, except additive printing machinery for producing three-dimensional products;
      (v) low-voltage switchgear and control gear;
      (vi) electric motors;
    (q) the following high-voltage electrical products:
      (i) switchgear and control gear;
      (ii) transformers.
    not sure if that helps
    Regards Mike.
  • Semantics indeed!. Actually it's both. We have several standards we have to comply by in our requirements, one of which points to compliance with BS7671 for the electrical system.
    This discussion has been very helpful. Thank you to all :-)
  • Is it an electrical installation or a machine? Or neither?? My first thought was whether this equipment is in scope or not. 110.1.1 says that the Regulations apply to electrical installations, so if it is not one, BS 7671 does not apply.
    Agreed.
    Is the device in question a "socket-outlet". Newfutile questioned this. I think that it is difficult to get away from the connexion being a socket and plug, but I am far from convinced that it is a "socket-outlet" as defined. More importantly, 411.3.3 is all about supplying electrical energy (the Grid in a building, PV, generator, WHY) from a socket upstream to an appliance downstream.
    I'm also not convinced it's definitely a "socket-outlet".
    however, this connector doesn't have an IEC, CENELEC or British standard ... so, to use them in an electrical installation for which BS 7671 applies (including those to BS 7909) would require a declaration of some sort (see BS 7671, Regulation 133.1.1 and Section 511).
    However, if BS 7671 is the standard to use, then this is still relevant ...
  • Yes, we have a declaration. BS7671 does not cover military 'equipment' but the clients stipulated compliance with certain Def-Stan's, one of which said we must comply with BS7671 for the electrical installation side of the 'equipment' where reasonably practicable.
    The connectors are a must have because of the use of the mobile equipment, and while they don't have an appropriate IEC, CENELEC or BS the design specifications make it very safe for our purposes and will not result in a lesser degree of safety it complies under section 511.
    I agree that while it is a socket I am also not convinced it can be defined as a socket-outlet. Hence the question, as opinion is a little divided here because of the combined use and architecture it is a bit of a grey area that isn't specifically covered  by any of the standards.
    As much as I would prefer the belt and braces approach of a 30mA limit, the added complication of the current transformer windings reducing the set trip current to just under half makes it difficult to ascertain if an actual trip current of 30mA would cope with the inrush currents.
    The adjustable RCD has detents at 0.03, 0.1, 0.3, 0.5..... so we can test at 100mA which will give a trip current of around 45mA. I don't know if this was done at the Dev stage because there are no notes of any kind. When I spoke to my predecessor about it, it was 7 years after the fact so the details were a bit, shall we say murky.
  • if an actual trip current of 30mA would cope with the inrush currents.
    Can you tell if the inrush current has a significant "leakage" component? There have been quite a few reports of RCDs tripping on switch-on, not because there's a particularly large earth leakage (residual) current during switch-on, but rather the L-N currents get large enough to saturate the sense coils/ferrite , which then don't entirely balance and trips the RCD. Sometimes selecting a RCD with a larger current carrying rating (In) (as distinct from the residual current rating IΔn) can help solve that problem without reducing the level of protection.
    Similarly I have heard tell of some nuisance trip resistant 30mA RCDs which as well as some extra filtering incorporate a slight delay although - but still open within the requirements for additional protection. Might be worth a look.
  • The inrush when the charging system is engaged trips the RCD when it is set to 30mA.
    Why is the inrush so 'large', and has anyone measured the actual inrush?
    Maybe just needs a large soft iron 'ferrite bead' on the appropriate cores to either slow down that surge, or keep the 'leakage' surge in the correct [return path] cores.
    You may have a common-earth/ground problem on the DC equipment side that looks just like "diverted neutral" where superfluous bonding provides alternative paths.
  • if you try the 100ma (really 50ma in this case) setting, also set the 0,1 second delay at the same time. - the delay is not long enough to seriously impact the shock survival risk, but the worst of any start-up surge should be over before the device unlatches. Of course the leakage could be too high in the steady state too, but it is a fast way to find out.
    What a surfeit of weasel words!
    I don't see 110.2 excluding military equipment, but if the equipment is used overseas, is BS 7671 relevant? Which national law applies? Then of course, there is the fog of war and doing your very best in the circumstances.
    Against that, as I previously suggested, if the equipment is used in UK (or other NATO) exercise areas, BS 7671 and indeed other H&S law will apply.
  • If BS 7671 must be used, it does not matter whether the circuit has a socket-outlet, if the equipment is (or could be) used outdoors.
    Circuits for mobile equipment for use outdoors with rated current less than 32 A must be protected by 30 mA RCD in AC systems, and exceptions are not permitted ... Regulation 411.3.3
  • OK the no 13 size back-shell in that part no is the commercial equivalent (that's from the 'TV' ) to a mil spec 'C' body size, with pin pattern 4 narrows it down to these. The 4 pins are AWG 16, and the P on the end is the plug - an S is the socket...
    Of the types it could be that is a good one.
    If the live socket turns off by interlock when the plug is removed, as one of them is acting as a pilot wire, that is even better.