Permanent Lighting in industrial environment with strong vibration

Good morning everyone,

are there any suggestions on installation of permanent lighting in areas with strong vibration?

In particular, I am searching for adequate installation methods on walkways above fans in the cooling condenser areas. Fans are responsible for strong vibration all year round, the whole steel structure is shaking and traditional bracketry seems to fail at fast rate.

Consider that the walkway to be illuminated has a handrail on both sides but no other structural steel or walls are available because the roof can't be used for lighting support.

Kind regards

Parents
  • Are you able to share any images, to help paint the picture? 

     

    Can light fittings be clamped to the handrail? If only the walkway floor is to be illuminated, you don't necessarily need to have a fitting mounted above. It could be mounted horizontally.

Reply
  • Are you able to share any images, to help paint the picture? 

     

    Can light fittings be clamped to the handrail? If only the walkway floor is to be illuminated, you don't necessarily need to have a fitting mounted above. It could be mounted horizontally.