I’d like to ask for some advice on an unusual EICR observation. Domestic bungalow, the installation has the main consumer unit installed in the external meter box, the recessed kind.
Ive paid attention to opinions of others over the years as this certainly isn’t a new subject and theres plenty of opinion on Google about it. Unless I’ve missed something obvious a general consensus seems to be that putting a consumer unit in a meter box might be frowned on by the suppliers who may need the space for their equipment, but from a BS7671 point of view there aren’t any specific requirements that would prohibit it so long as the box maintains the correct IP rating.
And then I found myself there in the pouring rain, wind lashing rain drops right into the consumer unit while I was trying to get a Ze reading… And I thought to myself this right now is dangerous. I’m at risk of electric shock and none of this equipment is type tested for get wet in any way, an explosive short of the main switches live terminals seemed inevitable if I continued. In the short term I felt it necessary to close the lid and wait… and wait….
So now I’m asking myself does this experience justify a C2? Regulation 513. requires that “every item of equipment shall be arranged so as to facilitate its operation, inspection and maintenance and access to each connection. Regulation 522.3.1 requires that “a wiring system shall be selected and erected so that no damage is caused by condensation or ingress of water during installation, use and maintenance. I felt it was dangerous to inspect and maintain that consumer unit in that location under those environmental conditions. I also feel it may be a concern for old Mrs Smith (not her real name) to go outside in a storm and try to reset an RCD or isolate a circuit if there as a problem, I’d feel more forgiving it it were an industrial location where only skilled or instructed people require access, but this is old Mrs Smith in her bungalow here.
edit also 529.3 requires “Provision shall be made for safe and adequate access to all live parts of a wiring system which may require maintenance.
Has anyone else had to provide an EICR under similar circumstances? Does any one have any advice on how they may code this on an EICR? And does anyone want to offer any other requirements from BS76171 for me to also consider?
Thanks for your opinions in advance.