SPD - cable selection
Hi all, just out of curiosity, trying to establish if I’m completly
overthinking this. There is an existing type 1/2 SPD installed on a main mccb panel. It’s fed from a 63A mccb and is approx 30cm away and goes into a separate enclosure.
the cable size is 10mm with a 16mm earth. Iv been wondering regarding the 63A mccb, but am I right in thinking it’s only there to provide short circuit protection rather than overload?
  • am I right in thinking it’s only there to provide short circuit protection rather than overload?
    The 2nd half of 534.4.10 would seem to agree!
  • One hopes that there is almost no current in the MCB or the wiring to it, most of the time. The only times there is would be
    1) by design for some microseconds during a transient over-voltage when a few kA might flow and the SPD dissipates at peak perhaps hundreds of kW but only for a few microseconds,  and  thinking adiabatically, a wiring copper area of a few mm2 would probably do.
    2) When the SPD finally dies, if it does so in a short circuit sort of way, when the large current will only flow at most for the time to operate the breaker, if the SPD does not fuse first, and to be honest a thinner cable would probably be OK then as well...
    PS
    In terms of responding to fast edges for lower inductance,  and best clamping a pair of flat palm braids would be better than twins of  round wire ,but such things are not compatible with normal wiring terminals and methods.
  • or 3). when a fault (short) occurs on the wiring between the MCB and SPD...
  • "or 3)."
    Very true. A case where again, a thinner cable would probably suffice. There is no safe condition where 63 amps flows for very long at all, given the volume of the SPD itself and the absence of cooling air, water or rotating shafts to remove the energy.
  • In terms of responding to fast edges for lower inductance,  and best clamping a pair of flat palm braids would be better than twins of  round wire ,but such things are not compatible with normal wiring terminals and methods.
    It may not explain the relatively high rating of the MCB, but are the short and fat cables not required to minimize inductance, else the surge might, as it were, not be able to reach the SPD.
  • it is indeed all about the surface area of the copper - the outer 'skin' if you like. but if it was not so impractical, the centre of the wire could be replaced with empty space, or even craft cheese for all the effect it has on the high speed waveforms. Actually inductance per unit length is a reasonably gentle function of diameter, compared to resistance, and far more impedance reduction is to be gained by bringing the equal and opposite 'return' current as close as possible.
    This is because then the magnetic fields cancel in the region "far away", observed from which, the 2 currents appear more or less centred on the same line. The closer you can get the two currents to each other, the nearer that "we are far enough away so the rest of the magnetic field from here on out is cancelled " boundary gets, and the less voltage drop is needed to induce whatever close-in magnetic field remains having been not quite cancelled.
    There is quite a nice free calculator here
    https://k7mem.com/Ind_Wires_Strip.html
    that allows one to see the effect of bringing the ground return path close to a wire. Be aware that the defaults are inches and American wire gauges but with a bit of effort wires a sensible few mm in diameter and a metre long can be calculated as they are far away (many diameters) and close (perhaps a few mm)  from the return current path.
    regards Mike.
  • because then the magnetic fields cancel i the region "far away",
    And if you completely box it in, you get a microwave waveguide Grin.  (but that's taking it too far!)
  • Coaxial cable with the thinnest possible dielectric  is perhaps more practical in such cases where very low impedance and no external fields at all are the requirements-)
  • Especially as no electrons move in almost all these [AC] cases. It's the polarisation of free space Wink .
    (at 50 Hz, at the fusing current of copper, the 'electrons' move a mere fraction of an atomic spacing - it's just 'polarisation')
  • In the new Hager single-phase consumer unit there is not any circuit protection for the SPD  and there are not any cables connecting the SPD.
    Line and neutral to the SPD are connected into the main switch using busbars and the SPD is earthed to the consumer unit metalwork though a metal clip pop riveted to the Din rail.