Advice on coding dual (RCD) Residual Current Device board
A colleague of mine had come across a dual (RCD) Residual Current Device board with no spd,a solar pv system and a car charger.
this was installed around 2 years ago when built from new.
my understanding is that the evse cant be on a shared rcd neither can the solar.they are both type A rcd and the evse seems to have pen fault and dc protection built in.
  • I came across exactly the same on a very recent new build ( moved in this year ) yesterday while fitting them an external socket.
    The job couldn't possibly have been done any cheaper. The usual long meter tails from the meter box as well.
    Gary
  • To code something on an EICR I think you need to be able to refer back to a specific BS 7671 regulation.
    As far as I can see there's no requirement for a dedicated RCD for PV systems in section 712 (please do correct me if I've missed something!) - so the general requirements for a parallel generator apply - 551.7.1 (ii) demands DP switching (which your RCCB presumably provides, unlike some RCBOs) - but otherwise there doesn't seem to be a requirement for it not to be shared with other circuits (by disconnecting the N, in theory at least, the risk of shock to Earth is mitigated for all the downstream circuits even if a L-N voltage remains). Some guidance may well go beyond that, but I think that's difficult to justify as a code on a BS 7671 EICR. A note perhaps.
    Arguably the "protected individually" requirement for a a EV point applies to the charging point outlet, rather than the circuit that supplies the EVSE. If the charge point includes an RCD (or equivalent functionality) then I can see a point of view that the requirement is satisfied regardless of whether the supply circuit has no RCD at all or an  additional RCD that covers other circuits as well. There's nothing in the requirement to say there can't be extra RCDs upstream.
    You could argue about selectivity and the consequences of the operation of a single protective device, but for a domestic that'll be hard to prove I think.
  • my understanding is that the evse cant be on a shared rcd
    I think that Andy must be correct.
    ETA: notwithstanding anything in BS 7671, it occurs to me that the manufacturer's instructions may prohibit a shared circuit, and potentially, a shared RCD.
  • I  believe the code of practice for solar pv says it wont be shared.there has been discussions on here about that.
    i also wonder if the rcd will meet disconnection times as the inverter could overrun causing a short time islanding effect.i also wonder if the inverter is generating a lot of power the rcd is not so involved in the supply to the shared circuits.
    on the evse vehicle to home is now a thing .
    With the rcd i take it mean that each evse circuit shall be protected individually.
    in any case a dual rcd board with no spd installed in 2023 is not good workmanship in my opinion,just a money saving exercise.
     Solar PV into load side of RCD
     Dual RCD boards are unlikely to be suitable for EV charging installations even with type A or B RCDs, discuss
  • i also wonder if the rcd will meet disconnection times as the inverter could overrun causing a short time islanding effect.i also wonder if the inverter is generating a lot of power the rcd is not so involved in the supply to the shared circuits.
    The inverter can certainly keep running after the RCD opens - some early versions of G83 allow it to take 5s (possibly longer) after spotting "grid loss" before shutting down. I've seen the effect myself when my main switch was opened but the light in the room stayed on - causing great consternation for the visiting electrician. I had time to say "Ah, that'll be the solar panels - they should shut down in a few seconds" before it went off!
    Even if the load on the other circuits were to exactly match the PV output, and so there was no normal current flow through the RCD, the RCD would still "see" any earth fault/shock current as the N-PE link is on the supply side of the RCD and the fault on the load side - so to complete the circuit the full earth fault/shock current must pass unbalanced through the RCD even if none of the normal current does. So RCD should still strip normally in that respect.
    So we have a situation where the RCD should trip OK, but doing so won't necessarily remove voltage from the faulty circuit. Fortunately that's not quite as worrying as if first sounds. Conventional ADS isn't the only way to prevent electric shock - electrical separation also works (like for bathroom saver sockets, but in principle it can work equally well for larger systems) - and a long as the RCD opens N as well as L when it trips, all the downstream circuits should become separated from earth - hence the shock risk should be addressed.