How might the proposed changes to UK mains voltage limits affect older electrical infrastructure?

Hi all,
I’m looking for some expert insight into how proposed changes to UK mains voltage limits, particularly any shift away from the nominal 230 to 240 volt range, might affect older electrical infrastructure.
Our site is fed directly from a DNO transformer, although only two of its output connections are currently in use and we’re unsure how many it has in total. The infrastructure was originally designed and installed in the 1980s and includes legacy three-phase motors and analogue control systems that were built to operate on 240 volts single-phase and 440 volts three-phase.
We also have a step-down transformer that is fed by a three-phase 125 amp supply and provides 110 volts at 50 hertz. This is used to meet extra-low voltage requirements in our training environment. In addition, there is a separate system currently locked out that runs on 115 volts at 60 hertz, which is temporarily offline due to a failed frequency converter. This is scheduled for replacement shortly.
I’m particularly interested in understanding how any changes to mains voltage might affect the transformers themselves, both the DNO-fed unit and our internal step-down transformers. I would also appreciate any thoughts on the risks to analogue control systems calibrated for 240 and 440 volts, potential safety or compliance concerns from undervoltage or harmonics introduced by modern supply variations, and any practical mitigation strategies or retrofit options for mixed-voltage and mixed-frequency setups.
Any advice, experiences, or references to standards would be greatly appreciated.
Thanks in advance
Parents
  • This is a very pertinent question, particularly for legacy 1980s installations.

    Firstly, it is worth noting that the UK supply has been nominally 230 V since harmonisation, but in practice remains within the statutory tolerance defined in ESQCR and BS EN 50160 (typically 216–253 V). Therefore, most equipment originally designed for 240 V single-phase and 415/440 V three-phase has generally continued to operate without significant issues.

    Regarding transformers, both the DNO distribution transformer and internal step-down units are usually designed to accommodate ±10% voltage variation. The main concern would be thermal loading under sustained overvoltage conditions rather than immediate functional failure. Tap settings on the LV side may also be relevant if site voltage is consistently high.

    For legacy three-phase motors rated 440 V, operation on today’s nominal 400 V supply is typically acceptable, with only a modest reduction in torque margin. The more critical risks tend to arise from undervoltage effects on control circuits (relay chatter, contactor drop-out) rather than on the motors themselves.

    Analogue control systems calibrated for fixed 240/440 V supplies may indeed be more sensitive to modern power quality issues, particularly harmonics introduced by VSDs, UPS systems and EV charging. A power quality survey (voltage profile, THD, flicker) would be a sensible first step.

    In terms of mitigation, practical options include reviewing transformer tap positions, ensuring control transformers are correctly rated, and considering modernisation of critical analogue control components. Reference documents would include BS 7671, BS EN 50160 and IET Guidance Note 1/Power Quality.

    Overall, the change in nominal voltage itself is unlikely to be the primary issue — supply variation and power quality in mixed legacy/modern environments are usually the key factors.

Reply
  • This is a very pertinent question, particularly for legacy 1980s installations.

    Firstly, it is worth noting that the UK supply has been nominally 230 V since harmonisation, but in practice remains within the statutory tolerance defined in ESQCR and BS EN 50160 (typically 216–253 V). Therefore, most equipment originally designed for 240 V single-phase and 415/440 V three-phase has generally continued to operate without significant issues.

    Regarding transformers, both the DNO distribution transformer and internal step-down units are usually designed to accommodate ±10% voltage variation. The main concern would be thermal loading under sustained overvoltage conditions rather than immediate functional failure. Tap settings on the LV side may also be relevant if site voltage is consistently high.

    For legacy three-phase motors rated 440 V, operation on today’s nominal 400 V supply is typically acceptable, with only a modest reduction in torque margin. The more critical risks tend to arise from undervoltage effects on control circuits (relay chatter, contactor drop-out) rather than on the motors themselves.

    Analogue control systems calibrated for fixed 240/440 V supplies may indeed be more sensitive to modern power quality issues, particularly harmonics introduced by VSDs, UPS systems and EV charging. A power quality survey (voltage profile, THD, flicker) would be a sensible first step.

    In terms of mitigation, practical options include reviewing transformer tap positions, ensuring control transformers are correctly rated, and considering modernisation of critical analogue control components. Reference documents would include BS 7671, BS EN 50160 and IET Guidance Note 1/Power Quality.

    Overall, the change in nominal voltage itself is unlikely to be the primary issue — supply variation and power quality in mixed legacy/modern environments are usually the key factors.