Regulation 643.3.3 (ii) clarification

I want to ask if someone can help clarify the requirements on the regulation 643.3.3, notably the second para  (or ii in GN3)

Whilst it is understood that an initial insulation resistance test should be carried out with all Sensitive loads disconnected, once they are reconnected the regulation reads "Following connection of the equipment, a test at 250 V DC shall be applied between live conductors and the protective conductor connected to the earthing arrangement."

Does this mean we are conducting two separate tests, i.e. line to CPC and Neutral to CPC? Or a single test where we link line and neutral, then test that to CPC (i.e. like previous guidance). I suspect it is the letter, but would be grateful for your thoughts.

Parents
  • The IET OSG page 120 is much clearer when explaining the three-phase installation insulation resistance test.

    Quote “Test to earth from all live conductors (including neutral) connected together.”.

Reply
  • The IET OSG page 120 is much clearer when explaining the three-phase installation insulation resistance test.

    Quote “Test to earth from all live conductors (including neutral) connected together.”.

Children
  • Thank you, that's very helpful. The reason for my confusion is that I'm coming across increasing numbers of  fixed plug sockets with USB, Zigbee modules, cheap LEDs, etc and, whilst they are SELV components, they are part of a non-SELV circuit. So I'm never sure how to treat them. Especially when competing a minor work certificate or EICR and it isn't always reasonable (or possible) to disconnect every socket or light fitting.