I want to ask if someone can help clarify the requirements on the regulation 643.3.3, notably the second para (or ii in GN3)
Whilst it is understood that an initial insulation resistance test should be carried out with all Sensitive loads disconnected, once they are reconnected the regulation reads "Following connection of the equipment, a test at 250 V DC shall be applied between live conductors and the protective conductor connected to the earthing arrangement."
Does this mean we are conducting two separate tests, i.e. line to CPC and Neutral to CPC? Or a single test where we link line and neutral, then test that to CPC (i.e. like previous guidance). I suspect it is the letter, but would be grateful for your thoughts.