The question is about the compliance with IET regulation 710.415.2.2, which is included in Section 710 'Medical locations'.

It states that: 

the measured resistance between the earth terminal of any socket-outlet (or fixed equipment) and any extraneous-conductive-part shall not exceed 0.7 ohm.

(image extract below)

In clause 9.81, referred to, states:

(a) for IT, TN and TT systems, the voltage presented between simultaneously accessible exposed-conductive-parts and/or extraneous-conductive-parts shall not exceed 25 V a.c. or 60 V d.c.;

Note the International Standard IEC 60364-7-710 states the following:

Question 1 of 2 (question 2 in a separate post)

Hence I consider that the requirements for Group 1 are as below:

0.7Ω maximum resistance within the room between the terminals of the protective equipment conductor of socket outlets and fixed equipment and the EBB, and between any extraneous  conductive part and the EBB.

25v maximum touch voltage for systems operating at a.c.

Is this assumption correct?

Parents
  • I'm concerned this is a "1 of 2" ... The 'most onerous' of the requirements apply ... whatever the conditions. In the UK we apply BS 7671, and all of the requirements apply across the various conditions specified.

    It's not possible to assume that IEC(and CELENEC) documents can be rationalised directly into national codes.

    National conditions (SCNs) need to be taken into account when looking at IEC documents, 'special national conditions' (SCNs) when looking it CENELEC documents.

Reply
  • I'm concerned this is a "1 of 2" ... The 'most onerous' of the requirements apply ... whatever the conditions. In the UK we apply BS 7671, and all of the requirements apply across the various conditions specified.

    It's not possible to assume that IEC(and CELENEC) documents can be rationalised directly into national codes.

    National conditions (SCNs) need to be taken into account when looking at IEC documents, 'special national conditions' (SCNs) when looking it CENELEC documents.