Streetside metal feeder pillar with PME supply

Hi,

I’m looking at what I assume must be a reasonably common situation, particularly with older installations, where a streetside metal feeder pillar supplying EV charge points has a PME supply and an O-PEN device is installed within the DB.

The bonding conductor from the MET to the feeder pillar is before the O-PEN device, so under PEN fault conditions the outgoing circuits will disconnect but the feeder pillar will rise in potential and will not disconnect from the supply.

Regulation 411.4.2 talks about the recommendation of installing an additional earth electrode on TN systems at the MET. Is this a feasible option to reduce the touch voltage on the feeder pillar under PEN fault conditions, if you could get a low enough resistance on the electrode? Or are there any other options other than replacing, or installing a GRP feeder pillar in the first place? Or a front-end type O-PEN device?

Thanks