Large panel distribution board, with all three front doors not opening fully because they hit the tray and lights.
Would you classify it as C2 or C3?

Large panel distribution board, with all three front doors not opening fully because they hit the tray and lights.
Would you classify it as C2 or C3?

Large panel distribution board, with all three front doors not opening fully because they hit the tray and lights.
Would you classify it as C2 or C3?
More importantly, this situation might well constitute a breach of legislation ... Regulation 15 of the Electricity at Work Regulations and/or Regulation 9(2) of the CDM Regulations.
It can lead to a LIM for a periodic inspection and test ... The inspection and test is an activity within the scope of the CDM Regulations.
Legislation over-rides BS 7671, and this situation should be addressed with the dutyholder as a matter of urgency.
Large panel distribution board, with all three front doors not opening fully because they hit the tray and lights.
Would you classify it as C2 or C3?
More importantly, this situation might well constitute a breach of legislation ... Regulation 15 of the Electricity at Work Regulations and/or Regulation 9(2) of the CDM Regulations.
It can lead to a LIM for a periodic inspection and test ... The inspection and test is an activity within the scope of the CDM Regulations.
Legislation over-rides BS 7671, and this situation should be addressed with the dutyholder as a matter of urgency.