Is 20 ohm earth electrode resistance required for back up supply?

A landfill site supplied from private transformer has asked us to connect a back up generator to a changeover switch in the weighbridge. I’ve had a look at BS7430 7.2.1 and it says an earth electrode with resistance of 20ohms or less is required. This is potentially quite difficult to achieve. It is a lot lower than the BS7671 requirement to be considered reliable. What is the reason for such a low figure and does it apply equally to private supplies as public supplies?

  • The risk that arises is that the fault to true earth connects genset live to the ground beneath the feet.

    Arguably that situation is similar to when someone picks up damaged flex outdoors on a conventional TN or TT system. In theory it shouldn't happen as the live conductors should be surrounded by the equivalent of double or reinforced insulation suitable for the conditions (e.g. sheathed flexes) (or some situations possibly even flexes with a concentric earth (CY or SY types for example)), but if it does happen we're happy to wait until someone gets a shock and rely on additional protection by ≤30mA RCD to disconnect.

    The RCD might trip early, is there's sufficient contact between the exposed live conductor and terra firma before it's picked up.  Or it might not and have to wait until someone touches the damaged section of flex. Or it might not even then if all the resistances conspire to keep the current flow below 30mA (hopefully then the harm from the shock is limited though).

    On an unearthed system with a N-c.p.c. link, and a  ≤30mA RCD downstream of the link, the risks might be similar - while a L-terra firma fault may well not trip the RCD immediately, it should if the circuit is completed by someone in contact with the ground touching an exposed-conductive-part (where sufficient current flows to be a risk to life).

       - Andy.