Is 20 ohm earth electrode resistance required for back up supply?
A landfill site supplied from private transformer has asked us to connect a back up generator to a changeover switch in the weighbridge. I’ve had a look at BS7430 7.2.1 and it says an earth electrode with resistance of 20ohms or less is required. This is potentially quite difficult to achieve. It is a lot lower than the BS7671 requirement to be considered reliable. What is the reason for such a low figure and does it apply equally to private supplies as public supplies?
  • First thought - doe the transformer have its own LV electrode? If so, it's presumably already got an electrode with less than 20 Ohms resistance and as it's a private transformer, that electrode is presumably yours rather than the DNOs. So could you rely on that for the backup generator? OK there might be some limitations - e.g. you couldn't run the generator while the connection to the transformer electrode is broken (as might be the case during maintenance such as the replacement of the transformer or its connections) but that's all under your control rather than being some unknown as with normal DNO earthing facilities during a power cut.
    But back to the original question... Why 20 Ohms? - that indeed has been asked many times and no-one has come up with a theory as to how it was calculated - it's not related to the voltage or size of the supply or load, or potential leakage or fault currents - but rather seems to be the outcome of historical custom and practice. The chosen value does have some implications though - e.g. if the system supplies a TT'd subsystem, increasing the source electrode's resistance will result in higher loop impedances for the TT part (e.g the 21Ohms rule of thumb for the supply side of the loop no longer works), and higher step voltage around the source electrode. But things could easily be re-calculated for some other resistance. Certainly for some smaller systems (e.g. home generators/energy storage systems) higher electrode resistances have been deemed OK in guidance (I can't remember the exact values recommended and I think it differs in different circumstances)
  • In terms of danger, it all rather depends on what current is going to be required to pass through the electrode in the largest fault you might not be able to detect. If for example everything is behind a 100mA or 300mA RCD, as well it might be in a modern set-up you may consider 100mA or 300mA as the largest un-detected fault that won't ever trip, and say that you want no more than 50V of earth potential rise (tingle voltage to true ground) if that happens. This leads to nearer 150 ohms for the 300mA case and 400 ohms for the 100mA.  But, those would be an absolute upper bound, and some allowance must be made for degradation with dry weather, corrosion etc, so advice then ends up being to aim for 100 ohms or less.
    The 20 ohm figure goes back to  non-RCD protected distribution, and js very much a compromise value - it is used for small pole-pig transformers as it is achievable with electrodes that are spikes or laid in the local trench, but in reality the current available could keep the electrode live all day with a good enough fault. Big substations aim for 1 ohm or less, where possible, but again there is a limit to the achievable .
    How big is the generator ? - there is a sort of scale consideration here,  a wheelbarrow genset of few kW supplying one site hut with a single spike at 100 ohms is probably credible, but to put in say a dedicated 100kVA for a largish area with many buildings, without at the same time getting the digger drive to punch in a few scaffold poles in the corners of the concrete pad of the generator shed is a bit remiss !
    Generally the larger the area served, the better the earth needs to be or odd things can  happen, See https://engx.theiet.org/f/wiring-and-regulations/23375/rcd-failure-causes-shock-in-neighbours-house?pifragment-2370=3 for an example of the sort of thing.
  • I'm thinking if the weighbridge is of the pit type, with frame sunk into the ground, it would itself provide a low resistance.
  • It is a lot lower than the BS7671 requirement to be considered reliable.
    That statement of reliability actually comes from BS 7430 ... note that BS 7671 doesn't really cover any specific requirements for earthing a 'source of supply', the correct standard for this is BS 7430.
    Indeed it does at the moment.
    You might be interested in the alternatives, under certain circumstances, that are proposed in the draft for public comment of the next edition of BS 7430. If the relevant conditions are met, you might be able to get away with more than 20 ohms ... BUT ... this is a draft. See https://standardsdevelopment.bsigroup.com/projects/2023-01701
    You haven't provided some important information for us to be able to help further;
    1. What is the rating of the backup generator?
    2. What is the earthing arrangement intended to be in 'island' mode (where the backup generator supplies all, or part of, the installation when the grid supply is lost)?
  • The back up generator they have on site and wish to use is a Hyundai DHY6000SE. 5.2kw  6kvaThe manual seems to show overload protection of some sort but no indication of any earth leakage device. I am told the star point is connected to the chassis and the earths of the socket outlets and obviously is to be connected to the earth electrode although originally it may have been floating. It is proposed that it is connected to the changeover switch by an appliance inlet and a short trailing lead plugged into the generator.
    The supply from the transformer is tns. It supplies a large section of the site but the back up generator is only proposed to be used for the weighbridge portacabin which has a small CU protected by 30mA rcd main switch. The loads are sockets lights, heaters, the bridge itself, some small floodlights and traffic lights. The main reason for the supply being off would be issues on the generation side (the site generates electricity from landfill gas). So mostly the earth connection at the supply transformer would remain in place but it is possible that maintenance work on the transformer would mean it being disconnected so would not want to rely on it.
  • II was reading 7.2.5 as meaning all generators acting as a back up changeover supply have to be earthed generators and come under section 7.2 . Does it  actually specify the requirements where an earthed generator is being used but not preclude using an unearthed generator as a back up changeover supply where it is below 10kw, meeting the requirements of  section 7.1 ?
    It’s a single phase generator, obviously no star point.
  • Using a separated (unearthed) system for small generators is indeed a possibility, and often done with small portable setups - e.g. a genny and one power tool, but it gets tricker where you're supplying multiple appliances (you fall into BS 7671 section 418.3 so is limited to where the installation is under the control or supervision of skilled/instructed persons. It also gets dubious with multiple Class I appliances with filters that can allow currents to flow from exposed conductive parts back into system.
    So, at that fault level, what is providing automatic disconnection of supply for protection against electric shock? Usually, we'd revert to RCD protection i.e. all circuits that are energised in 'island mode' are supplied by RCD or RCBO, but still form TN-S for the generator?
    if that is the case, there's an approach in the IET Code of Practice for Electrical Energy Storage Systems (or the IET Electrician's Guide to Domestic Electrical Energy Storage Systems), which permits higher earth electrode resistances, in some cases up to 200 ohms ... although note that some RCBO's require an earth resistance of 100 ohms maximum.
    If this approach is used, the recommended maximum earth electrode resistance depends on the largest residual current rating of all RCDs protecting circuits in island mode. This approach is proposed in the latest draft for public comment (2025) for the next edition of BS 7430 ... but it's not in BS 7430 yet.
  • Actually as soon as you have more than one class 1 (earthed) item, unless  all the installation inside one equipotential class 1 zone, the idea of a genset with a neutral earth bond but without a local electrode gets a bit shaky. That said I am well aware that this is the state for nearly every 'burger van' installation with a portable generator sitting in a puddle out the back. It's OK,  until the cable leaves the van for a set of festoon lights for a seating area or something.
    The risk that arises is that the fault to true earth connects genset live to the ground beneath the feet. The problem is that all the CPCs and the burger van or whatever, are 230V away from this, , but in the absence of a path between generator neutral and earth (as Graham calls it Earth with a big E, the terra-firma kind, not the CPC) the fault goes un-noticed, until a second non-fault like a person competes the loop.
    Very small, single power tool type arrangements are better off without an NE bond, and without an electrode - rather like the shaver transformer concept. As soon as you have more than one appliance that is not double insulated you really need the NE bond, and very few cases where you have that do you not need some sort of electrode.
    There are some nice diagrams in that draft standard actually, and its nice to see the advice catching up with what is actually now quite common practice. The bigger problem is that most folk will probably never see it.
  • Note that if the wiring diagram in the manual here https://hyundaipowerequipment.co.uk/6.7kva-silenced-standby-single-phase-diesel-generator-dhy6000se/  is correct
    there is no internal N-E bond, and all windings are floating. You will need one to make an RCD work, and you will need an RCD, as it won't be able to reliably clear 32A breaker in the safety of life time.