If you were to do a Type A RCD test on the RCDs installed in the consumer unit, what test current does the installation tester deliver?

If you were to do a Type A RCD test on the RCDs installed in the consumer unit, what test current does the installation tester deliver?
Would that not depend on whether you were '. . . doing a Type A RCD test' or '. . . testing a Type A RCD in accordance with BS 7671 (643.7.1) and/or (643.8)' ?
In the former case it would be an AC waveform with superimposed pulsed DC whilst in the latter case it would be an AC waveform.
- Ross
As in the photo, what amperage is the pulsed DC current test current that the tester will deliver for a X1 30 mA Type A RCD test?
A multiplier of 1.4 comes to mind, so with the instrument set as in the photo (30 mA × 1 × 1.4) = 42 mA ?
- Ross
1.414 the square root of 2, so 42.42 mA.
I thought that A type RCDs only needed to cope with 6mA of d.c.?
- Andy.
Hang on. BS 7671 643.8 specifies, "alternating current test at rated residual operating current (IΔn)". No more, no less.
ETA: your instrument's calibration certificate will show the actual current which it delivers.
Hang on. BS 7671 643.8 specifies, "alternating current test at rated residual operating current (IΔn)". No more, no less.
ETA: your instrument's calibration certificate will show the actual current which it delivers.
Hang on. BS 7671 643.8 specifies, "alternating current test at rated residual operating current (IΔn)". No more, no less.
Recall however that:
- Ross
There is a good summary of the requirements for RCD testing in accordance with BS 7671 in Issue 91 (July 2022) of the IET Wiring Matters magazine:
- Ross